Thread: lack of velocity

  1. #1
    Join Date
    Jan 2008
    Posts
    13
    Post Likes

    lack of velocity

    Have a carrier 90% forced air nat gas system that was installed in 1992 by previous home owner. We've been here three years and this year no velocity coming from ducts. Can't get house ove 69 degrees here in Michigan. Replaced 4 inch filter, servcieman replaced inducer motor (it locked up), and checked system said all is ok. Blower works, flame burns. just not getting air out of the ducts. Dampers are open. Hot air duct above furnace is cool to touch. Any thoughts? Thanks

  2. #2
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,115
    Post Likes
    By your symptoms no air flow this year, furnace running can't get above 69 in house, I would think your furnace should be cycling on high limit. Secondary heat exchanger or evaporator dirty, or blower or all three. The furnace cabinet should be hot.

  3. #3
    Join Date
    Sep 2006
    Posts
    1,255
    Post Likes
    Do you have an A/C coil above the furnace? If so it may be clogged and restricting air flow.

  4. #4
    Join Date
    Jan 2008
    Posts
    13
    Post Likes
    Thread Starter

    no velocity

    thanks, your replies make sense, do have CA. Wouldn't 4 inch air filter trapped debris?

  5. #5
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,115
    Post Likes
    Quote Originally Posted by milender View Post
    thanks, your replies make sense, do have CA. Wouldn't 4 inch air filter trapped debris?
    You could have air leakage around the filter and 15+ years.

  6. #6
    Join Date
    Jan 2008
    Posts
    13
    Post Likes
    Thread Starter
    Is the cleaning normally done by the HVAC guy or one of the "duct Cleaning" companies?

  7. #7
    Join Date
    Jul 2001
    Posts
    3,112
    Post Likes
    Was the blower motor changed in the past? The rotation could be wrong.

  8. #8
    Join Date
    Jan 2008
    Posts
    13
    Post Likes
    Thread Starter
    Inducer motor was replaced two weeks ago but not blower motor. Could blower connection be reversed in disassembly and reassembly? Work was done by licensed HVAC company.

  9. #9
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    Quote Originally Posted by milender View Post
    Hot air duct above furnace is cool to touch. Any thoughts? Thanks

    Are you sure the a/c and heat are not both running at the same time?
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




  10. #10
    Join Date
    Jan 2008
    Posts
    13
    Post Likes
    Thread Starter
    outdoor air unit is not running. If it was would it restrict air flow to ducts? I'm getting heat at the ducts, but no velocity. Thanks

  11. #11
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    Quote Originally Posted by milender View Post
    outdoor air unit is not running. If it was would it restrict air flow to ducts? Thanks

    Yes if the coil was froze up or freezing up.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




  12. #12
    Join Date
    Jan 2008
    Posts
    13
    Post Likes
    Thread Starter
    Inspected A coil, no freeze up, no build up, vac'd it out anyway. No improvement. Thanks. Some one mentioned blower running backwards, mine rotates clockwise looking from the filter.

  13. #13
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Not knowing what furnace you have, or which side the air filter is on, can't tell if thats teh correct rotation or not.

    When you looked to see if the coil is clean. Did you look on the side toward the blower,or the side toward the ducts.

  14. #14
    Join Date
    Jan 2008
    Posts
    13
    Post Likes
    Thread Starter
    Hi thanks, looked at both on the fan side and the duct side. Held a flashight in the a coil and could see the light from the other side. Didn't have much access to check every square inch though. Model number of furnace: Carrier Weathermaker 58SXC060 Series 100 installed in 1992. FYI put a temp probe in my vents in my office at home 66 degrees in the cold air return and 82 coming out the heat vent, but no velocity not getting the house over 67 degrees. Believe it was in the teens here last night.

  15. #15
    Join Date
    Aug 2007
    Location
    Atlanta, Ga
    Posts
    213
    Post Likes
    Has the duct work come apart somewhere...no velocity in any supply?


    If the unit is in the attic, is the attic warm?

  16. #16
    Join Date
    Jan 2008
    Posts
    13
    Post Likes
    Thread Starter
    Hi, unit is in the basement, can see the duct work all ok, basement is cold also, normally warmer there when furnace worked. Thanks.

  17. #17
    Join Date
    Jul 2001
    Location
    VA
    Posts
    2,801
    Post Likes
    You need to call somebody.
    ___________________________________________


  18. #18
    Join Date
    Jan 2008
    Posts
    13
    Post Likes
    Thread Starter
    Thanks, he's coming out tomorraw afternoon Will update as soon as.

  19. #19
    Join Date
    Jul 2001
    Location
    VA
    Posts
    2,801
    Post Likes
    Good, the air is doing one of two things... going somewhere it shouldn't, or not moving at all.... If it isnt moving at all, where is the heat all going? This is why I say it needs a first hand look.
    ___________________________________________


  20. #20
    Join Date
    Jan 2008
    Posts
    13
    Post Likes
    Thread Starter
    Hate to be the boy calling wolf, but guess my "no velocity" isn't the HVAC version of 'No Velocity." Tech brought a meter with a fan on the end of the stick (sorry for the technical terms) and tested the heat vents and said that he read 200 CFM(?) + and that, I believe, 150 is minimum expected, so velocity is fine. He then tested the temp with a meter and sensor at the cold air inlet above the furnace at 67 degrees, and on the hot air side at 82 degrees. He said my problem is lack of insulation in the walls and ceiling and that the air is too cold going into the furnace. Blower is running on low of three speeds. So I guess I'm back where I started. 34 degrees outside and can't get house over 68 degrees. Again in my first explanantion we didn't have this trouble over the last three winters. So I'm at a loss. Furnace keeps running flame on. Guess I think that the heat rise should be higher then 15 degrees. Any insight on that? Thanks for all responces.

Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •