    Have a carrier 90% forced air nat gas system that was installed in 1992 by previous home owner. We've been here three years and this year no velocity coming from ducts. Can't get house ove 69 degrees here in Michigan. Replaced 4 inch filter, servcieman replaced inducer motor (it locked up), and checked system said all is ok. Blower works, flame burns. just not getting air out of the ducts. Dampers are open. Hot air duct above furnace is cool to touch. Any thoughts? Thanks
    By your symptoms no air flow this year, furnace running can't get above 69 in house, I would think your furnace should be cycling on high limit. Secondary heat exchanger or evaporator dirty, or blower or all three. The furnace cabinet should be hot.
    Sep 2006
    Do you have an A/C coil above the furnace? If so it may be clogged and restricting air flow.
    no velocity
    thanks, your replies make sense, do have CA. Wouldn't 4 inch air filter trapped debris?
    Quote Originally Posted by milender View Post
    You could have air leakage around the filter and 15+ years.
    Is the cleaning normally done by the HVAC guy or one of the "duct Cleaning" companies?
    Jul 2001
    Was the blower motor changed in the past? The rotation could be wrong.
    Inducer motor was replaced two weeks ago but not blower motor. Could blower connection be reversed in disassembly and reassembly? Work was done by licensed HVAC company.
    Houston,Tx.
    Are you sure the a/c and heat are not both running at the same time?
    outdoor air unit is not running. If it was would it restrict air flow to ducts? I'm getting heat at the ducts, but no velocity. Thanks
    Houston,Tx.
    outdoor air unit is not running. If it was would it restrict air flow to ducts? Thanks
    Yes if the coil was froze up or freezing up.
    Inspected A coil, no freeze up, no build up, vac'd it out anyway. No improvement. Thanks. Some one mentioned blower running backwards, mine rotates clockwise looking from the filter.
    Not knowing what furnace you have, or which side the air filter is on, can't tell if thats teh correct rotation or not.
    When you looked to see if the coil is clean. Did you look on the side toward the blower,or the side toward the ducts.