Thread: Ducane gas

  1. #1
    Join Date
    Dec 2007
    Location
    Louisiana
    Posts
    48
    Post Likes

    Ducane gas

    I just installed a Ducane 100,000 btu gas furnace. Got a call 3 days later it wasn't working. Went over and the ignigter was out. Got a new one installed it. Everything fine. 3 days later got a call, the heat wasn't working. Went back and the ignigter was out again. Checked the voltage and am getting 130 volts to the ignigter and the furnace. Is this too much voltage?

    Thanks,
    T

  2. #2
    Join Date
    Dec 2007
    Posts
    18
    Post Likes
    Is it a hot surface ignitor?

  3. #3
    Join Date
    Aug 2002
    Location
    Southern NJ
    Posts
    962
    Post Likes
    Is the ignitor dis-engaging after flame is proven (or timing out by the board)?

    A little more info would be nice........
    I love to Cook...HVAC is a hobby that pays the bills!

  4. #4
    Join Date
    Dec 2007
    Location
    Louisiana
    Posts
    48
    Post Likes
    Thread Starter
    yes, It's cutting off and working like a champ. It works fine for about 3 days and quits. I checked the voltage again and when the board calls for the ignitor to fire, it spikes up to 140 volts and then slowly goes down to 130 volts.