Results 1 to 13 of 15
    Hyderabad, India
    Air handling Unit sizing
    Can some one guide me on accurate sizing an AHU. 1.5 air changes /hr ? is that right value for an office space? or 8 lit/person?
    thanks
    Kurrodu
    Nov 2007
    Quote Originally Posted by kurrodu View Post
    thanks
    Kurrodu
    If you're looking for "accurate sizing", throw out any rules of thumb (i.e. air changes, CFM/SF, SF/ton...etc).
    You have to start perform heating & cooling load calculations for the space/building. And unless you're a very quick learner, forget about trying to do this cold! If you're a contractor, team up with a seasoned HVAC consulting engineer.
    Hyderabad, India
    AHU Sizing
    I did the heat loads using design builder for a 1000 sqmt office space divided into 4 equal zones.
    It has a cooling load of 100 W/sqmt
    So I plan on using 40 TR Chiller. I think I need to use 1 AHU for each zone making it 4 AHU units
    So how do I go about sizing the AHU now
    Jul 2002
    Slacking off right now
    you can't be serious can you?
    I ain't going to provide any info - pay mech engineer to do the proper design and load calcs for a 11,000 sqft space
    what if It doesn't work what if the loads you calculated are wrong what if this is in florida or some where else thats closr to the equator
    based upon you working in metric I'd say this is likely to be other than north america.
    I'll say this right now the cubic air per minute standard in North America per ton of cooling capacity is cubic feet per minute
    This may not apply to the equipment available to you
    Also I did a basic calc based upon the sq ft you stated and I think you are off a bit - so much is going to depend upon where the building actually is - the glass size and amount - the internal staff/equipment load
    A chiller/ahu combination is something that needs correct calculations and some one whom knows what they are doing locally - get it wrong and you are up the creek
    www.vetopropac.com - The best tool bags on the market - The offical tool bag of choice by techs everywhere
    Arguing with some people is like wrestling a pig - eventually you realise the pig actually enjoys it
    Gonads serve a useful purpose but are no substitute for brains
    Jul 2002
    get the design specs for the ahus you have chosen and get an engineer to assist wit hthe project
    Hyderabad, India
    Thank you
    Quote Originally Posted by The Penguin View Post
    Hey thanks for the feedback. I am a mech engineer my self learning just graduated from ASU. I am doing this project on paper trying to learn. In reality this is not a project that I am going to execute.
    Thank you
    Jul 2002
    you need to lay out the ducting and load -assuming its equal loads per ahu you need ahus capable of 40tons cooling in total based upon your selection of 40 ton chiller capacity
    Don't forget a margin error +/- % - its damm hard to get more outa a ahu or a chiller than its to get less.
    If you are an engineer you should be able to buy a text book covering this kind of thing and understand it
    SW FL
    Cool
    100 * 1000 = 100,000 W = 341,300 BTUh = 28 Tons
    30 Ton chiller is needed, NOT 40.
    28 Ton /4 AHU = 7 TR / AHU
    or as specifically stated in the Load Calc for each zone.
    Designer Dan
    SW FL
    Question O.A. Requirements
    What does the Mechanical Code for Your state require?
    Most U.S. state codes have adopted ASHRAE 62.1.
    Your state or country could use something else.
    Designer Dan
    Jul 2002
    Quote Originally Posted by dan sw fl View Post
    I gurranty you he is in another country
    - I'm reluctant to provide more than general info as I fear he is sizing a real job
    also bear in mind his load pr sq metre may not atke into account infiltration so he may need that full 40 tons and then some if the job is close to the equator or other hot places
    SW FL
    I am a mech engineer my self learning (?) just graduated from A.S.U.
    What does A.S.U. stand for ?
    Why did you not register as a professional member on this site?
    Also, please complete contact info and group associations in your profile!
    Designer Dan
    SW FL
    A.C.H. : Air Change per Hour
    ... may not take into account infiltration so he may need that full 40 tons and then some
    O.A. was initially defined as 1.5 A.C.H.
    Designer Dan
    Hyderabad, India
    Dan,
    I am new to this HVAC-Talk forum. I will register as a professional member soon and A.S.U stands for Arizona State University.