    superheat on r-404a

    The walkin box I'm working on, trying to achieve -10 F (which it never had problems achieveing in the past).
    All of a sudden decided to creep up 5 degrees.
    Here are the readings.

    Head Pressure 250 psia (air temp. into condenser coil 77-78 F.)
    250 head pressure = 104 deg.F

    subcooling somewhere around 12-15 degrees F.

    Suction Pressure around 21-22 psia = -15 to -14 deg.f.
    Suction line temp. leaving evap. = -12 to -2 deg. F. (The temperature swing is -12 to -2) It stays quite stable. Isn't radical with the temp. swing.

    box temp. -5

    It's an empty walk in box about 7 x 10 foot square.

    At the moment its gone into a defrost cycle for maybe 20-25 minutes. (got a break thought I'd post this)

    My conclusion: When I first checked the superheat it was rediculously high. perhaps 25 degree S.H. So I've been slowly adjusting it the last few hours and I'm thinking the superheat setting is o.k. where it's at. I'm thinking since it's a low temp. the superheat can be a bit lower, thus the minimum 2 to 3 degree S.H.
    The suction has been slowly creeping down which gives me hope that it "may" eventually (perhaps overnight) reach the
    minus 10 setpoint. We'll see in the morning.

    I just wanted to run this by you guys to see if there is something I'm not seeing or thinking about.

    Thanks
    Mark

  2. #2
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,573
    Post Likes
    You probably have a pressure limiting powerhead on the txv. Best thing to do is leave it over night and check in the morning
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  3. #3
    Join Date
    Oct 2012
    Location
    Sandy, Utah
    Posts
    158
    Post Likes
    Thread Starter
    Thanks!
    I'm doing just that.....
    Going to check it in the morning.

  4. #4
    Join Date
    May 2003
    Location
    Utah
    Posts
    921
    Post Likes
    2-3 is pretty low considering there is some margin of error in the gauges and temperature meter. Plus, the SH you're reading on the outside of the pipe is not the true SH of the refrigerant inside the pipe.

    If you're reading 2, it might really be 1/2 or 1, and the compressor says that's just too close for comfort.

  5. #5
    Join Date
    Oct 2012
    Location
    Sandy, Utah
    Posts
    158
    Post Likes
    Thread Starter
    yeah,
    That's why I'm throwing this out there.
    I was thinking maybe with the low temp. that a swing to the minimum 3 deg. S.H. might be o.k.
    On the other end it gets up to 10 or 11 deg. S.H.
    I was concerned enough that I did my best to zero in "two" seperate gauges to hopefully get an accurate low pressure reading, but your right, it's hard to trust an absolute accurate reading with a guage.
    In your opinion, what do you think might be a safe minimum S.H. ?
    I appreciate your input.
    Mark

  6. #6
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,573
    Post Likes
    Quote Originally Posted by Mrak View Post
    yeah,
    That's why I'm throwing this out there.
    I was thinking maybe with the low temp. that a swing to the minimum 3 deg. S.H. might be o.k.
    On the other end it gets up to 10 or 11 deg. S.H.
    I was concerned enough that I did my best to zero in "two" seperate gauges to hopefully get an accurate low pressure reading, but your right, it's hard to trust an absolute accurate reading with a guage.
    In your opinion, what do you think might be a safe minimum S.H. ?
    I appreciate your input.
    Mark
    6-8. If the powerhead has a "P" on it it's pressure limiting. They take forever to pull down. Don't worry about it, just check it in the morning
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  7. #7
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,457
    Post Likes
    Quote Originally Posted by Mrak View Post
    yeah,
    That's why I'm throwing this out there. In your opinion, what do you think might be a safe minimum S.H. ?
    Much of that really depends on how close coupled the condensing unit is to the evaporator. And even then, if the condensing unit is on top of the evaporator, it's pretty hard to get liquid back to the compressor.

    But ultimately, once you get down to that -10*F range and lower, you often have to run higher superheats. You see, sometimes it has more to do with evaporator temp than how efficient the evaporator is working. So when you screw in the TEV adjustment, you lower the suction pressure, thereby running a colder evaporator. Just keep it in mind; sometimes these things are counter intuitive.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •