Thread: Liebert LP amd HPCO's - looking for your input here

  1. #1
    Join Date
    Apr 2008
    Posts
    360
    Post Likes

    Liebert LP amd HPCO's - looking for your input here

    I just had yet another failure - leaks in around the bellows, LPCO this time, and the loss of 100+lbs of 22.
    This is approximately 2000' vintage DS units. The last time this came up -a year ago, we had two leakers and checked them all, and ended up replacing four at the time.
    I'm considering replacement with something like the Mars module type;
    http://www.johnstonesupply.com/store...ep?pID=B16-941
    I don't recall seeing one of these ever leak or fail.
    Down sides?
    May not be wide enough C/O - C/I?
    What'd ya think?

  2. #2
    Join Date
    Jan 2007
    Location
    Charm City--the city that bleeds
    Posts
    2,788
    Post Likes
    Call it emerson and put in the "liebert "part. There aren't enough that fail to abandon the oem part. How fast can emerson flush this brand ?
    It's great to be alive and pumping oxygen!

  3. #3
    Join Date
    May 2010
    Posts
    308
    Post Likes
    Quote Originally Posted by The Doctor View Post
    Call it emerson and put in the "liebert "part. There aren't enough that fail to abandon the oem part. How fast can emerson flush this brand ?
    X2 Here.

  4. #4
    Join Date
    Dec 2006
    Location
    new england
    Posts
    791
    Post Likes
    I've found a few p66 fan cycling switches leaking on remote condensers. The lpc and p66 are the first 2 things I check when leak searching.
    Chaos equals cash$$$

  5. #5
    Join Date
    Apr 2008
    Posts
    360
    Post Likes
    Thread Starter
    Liebert rep says more or less, the same thing is in the P66 ('wiper instead of a two-position sw of course- I've only seen a few leaks there) and, he sells about ten a month (the LP/HPCO's) - i.e. like they're some kind of a 'wear part.. Lets see, oh yeah with hundreds of lbs of refrigerant at stake.

    Ok How about we start here..
    Anyone ever see one of these little module type switches fail/leak?


    BTW.. Steal Your Face
    Now that there's some country music ..Western Country
    Last edited by mixsit; 05-31-2014 at 09:12 PM.

  6. #6
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    We have had 3 XD systems blow their charge due to the cap tube type pressure switches. Vibrations snapped cap tubes loosing 240lbs r407c.

    It happens. If people did their job on PMs, it probably could be prevented.

    Sent from my SM-N900V using Tapatalk

  7. #7
    Join Date
    Dec 2001
    Posts
    1,365
    Post Likes
    I agree about pm's. We catch a lot of bellows failures on pm's. Usually before it even causes a noticeable change in the charge.

  8. #8
    Join Date
    Sep 2003
    Location
    Western PA
    Posts
    1,753
    Post Likes
    Quote Originally Posted by gravity View Post
    We have had 3 XD systems blow their charge due to the cap tube type pressure switches. Vibrations snapped cap tubes loosing 240lbs r407c.

    It happens. If people did their job on PMs, it probably could be prevented.

    Sent from my SM-N900V using Tapatalk
    I have to disagree. It's not the lack of PM's or people not doing there job on the PM. There is a real problem with 407C and bellows failures.

  9. #9
    Join Date
    Apr 2008
    Posts
    360
    Post Likes
    Thread Starter
    This unit (R-22 BTW) was healthy about a month ago when I was on it last.

  10. #10
    Join Date
    Apr 2008
    Posts
    360
    Post Likes
    Thread Starter
    Quote Originally Posted by targetman View Post
    I have to disagree. It's not the lack of PM's or people not doing there job on the PM. There is a real problem with 407C and bellows failures.
    Ya know I just realized something- ha! ironic (or telling maybe!) considering the questions I'm asking
    The 407 lieberts.. are using modular type high and low switches!

  11. #11
    Join Date
    Apr 2008
    Posts
    360
    Post Likes
    Thread Starter
    Quote Originally Posted by gravity View Post
    We have had 3 XD systems blow their charge due to the cap tube type pressure switches. Vibrations snapped cap tubes loosing 240lbs r407c.

    It happens. If people did their job on PMs, it probably could be prevented.

    Sent from my SM-N900V using Tapatalk
    Just to drum this home..
    Quote Originally Posted by mixsit View Post
    ...The last time this came up -a year ago, we had two leakers and checked them all, and ended up replacing four at the time.

  12. #12
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    I don't think it's 407c causing the problem. Has the same pressures as 22.


    Sent from my iPhone using Tapatalk

  13. #13
    Join Date
    Dec 2001
    Posts
    1,365
    Post Likes
    And the same failures with R22. Oil and refrigerant type so far seem to be irrelevant.

  14. #14
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    I would agree

    Sent from my SM-N900V using Tapatalk

  15. #15
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,459
    Post Likes
    Quote Originally Posted by targetman View Post
    I have to disagree. It's not the lack of PM's or people not doing there job on the PM. There is a real problem with 407C and bellows failures.
    Huh, that is a bit interesting. It seems I've changed out half a dozen dual pressure switches over the last three or four months. On 404a systems. All due to the bellows. Used to be you'd virtually never see a bellows failure. Maybe the stuff is being made in China instead of good ol' US of A.

  16. #16
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    Ive changed a bunch of p66 controls leaking in the bellows.

    Sent from my SM-N900V using Tapatalk

  17. #17
    Join Date
    Jan 2007
    Location
    Charm City--the city that bleeds
    Posts
    2,788
    Post Likes
    Anyone pm'ing lieberts without swiping the cap tubes with fingers to check for a blown bellows is not covering their bases. Of course, looking for abrasion points on cap tubes is also important, but between the p66 and the two inside the unit, there's no shortage of work over time.
    It's great to be alive and pumping oxygen!

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •