Outdoor HO Series Humidity/Temp Sensor
Does anyone have any hands on experience on this Veris Industries sensor? I'm getting a -43 for a temp reading and a -1 for a humidity input displayed at the DX9100. It's a transmitter sensor with a 4-20ma output. When I disconnect the temp circuit at the sensor it changes to -73. Started working on it late today so
I haven't had a chance to check the output. The transmitter range is -58 to 122. Outdoor temp was about 60.
Model # HO2XMSTA1If I tell you how long I have been in this business, would it really matter?
-
12-17-2007, 11:05 PM #2
Waiting Email Confirmation
- Join Date
- Dec 2006
- Posts
- 183
First, check to see if the jumpers on the back
of the DX-9100 are correct.
Check the program to see if defined and ranges are correct.
Check wiring:
one blue and one orange on 15vdc terminal of DX-9100.
Then blue on humidity AI and then orange on temp AI.
See following:
http://www.veris.com/file_uploads/ho_d.pdf
-
12-17-2007, 11:15 PM #3
Professional Member
- Join Date
- Sep 2003
- Posts
- 154
I think it has vac power supply and the wiring diagram states it must be vdc. This thing has been like this for over 3 years.
If I tell you how long I have been in this business, would it really matter?
-
12-19-2007, 09:56 AM #4
Professional Member
- Join Date
- Sep 2003
- Posts
- 154
Had the right dc input and the right jumper settings on xt module. Going to replace sensor. Will post results.
Thanks!If I tell you how long I have been in this business, would it really matter?
-
12-19-2007, 02:18 PM #5
Make sure to check the configuration of the AI in the GX9100 program. It should be configured as an active input, measurement units=1 (temperature) or 2 (%) for humidity, type of active input=1 (4-20mA), high and low ranges to match the sensor.
-
12-20-2007, 01:49 PM #6
Professional Member
- Join Date
- Sep 2003
- Posts
- 154
If I tell you how long I have been in this business, would it really matter?
-
12-20-2007, 04:10 PM #7
It also has to be set as an active input in the configuration of the AI. Active for volts or milliamps - passive for resistive.
-
01-20-2008, 09:05 PM #8
Professional Member
- Join Date
- Sep 2003
- Posts
- 154
Replaced control and had proper input to controller. Thanks for the help.
If I tell you how long I have been in this business, would it really matter?