Results 1 to 7 of 7
12-17-2007, 11:29 AM #1
- Feb 2007
- 7
Trane Tracer Summit v.11 to Tridium
Any way (LON, BACNET, OPC, etc.) I can monitor a Trane Tracer Summit system from Tridium, SoftJACE or otherwise?
Thanks!
12-19-2007, 05:05 PM #2
12-19-2007, 05:10 PM #3
- Feb 2007
- 7
12-19-2007, 05:22 PM #4
- Oct 2003
- Michigan
- 665
Any AI,AO,BI and BO created in the Summit database will be broadcast via Bacnet/IP and the Jace will be able to see them.
Beware of the prophet trying to make a profit.
There is less oxygen from knee level to the floor! Check it out next time you tie your boots.
12-19-2007, 07:34 PM #5
- Jun 2007
- Sydney, Australia
- 39
Learn the BCU
qtip is correct, using JDE (if using R2 Tridium) or AX quivalent you can learn the BCU and this will give you all the AI, AO, BO and BI. It is very straight forward. You should only need the Network ID used in the BCU which from memory defaults to 1.
Regards
12-19-2007, 08:42 PM #6
Member
- Feb 2007
- Cullowhee, NC
- 30
These guys have you on the right track, I have done the same thing on a college campus with a Tridium and Summit 16 system. However, not all points in Summit are created as Bacnet objects, a lot are points in devices without object IDs. For these, you can just create the appropriate (AI, BO, etc) object in the BCU and then Tridium willl pick them up on Bacnet. Let us know how it works!
12-19-2007, 08:43 PM #7
You will need to create points that have not already been created as AI AO BO BI, THis is due to the proprietary points, they are not broadcast as bacnet points, but instead comm 3, comm 4, or Lon. I would pull points into the Jace and then see if you are getting what You want. You however will need some one with summit access, to create the points and map them in. If there is a summit work station on site you can do this your self. Good luck it is not hard to pull it into the Jace using AX, the Jace sometimes is tricky getting all the settings to take, but once you do it works good.