    Taking over Honeywell motor

    Is there a way to take over a M9484 without buying a 135 ohm converter? How does this thing work inside? Does it send out a voltage/current? Can I successfully use two outputs for the B & W? Voltage or current? If my controller is trying to supply the current would that conflict? I am asking because I already have a controller there and this would be a 'no charge' promo. Seems like there's less than 2 volts on the terminals.

  2. #2
    Join Date
    Aug 2006
    Location
    New England
    Posts
    520
    There's a plug in module to convert it to 2-10VDC or 4-20mA. http://customer.honeywell.com/techli...0s/63-2235.pdf

  3. #3
    Join Date
    Oct 2006
    Posts
    191

    here ya go...

    You can use 2 output to drive the valve either direction.

    Open W and short R to B = drives open
    Open B and short R to W = drives closed