Results 1 to 8 of 8
  1. #1
    Join Date
    Jan 2006
    Location
    DFW Metroplex
    Posts
    4,910
    Post Likes

    Why Does The Breaker Keep Tripping?

    Got a call yesterday from a customer who tells me he keeps having to reset the breaker over and over - but the compressor keeps tripping the breaker.


    Geez - I wonder why?

    Last edited by markettech; 12-13-2007 at 11:58 PM.

  2. #2
    Join Date
    May 2004
    Posts
    12,477
    Post Likes

  3. #3
    Join Date
    Jan 2006
    Location
    DFW Metroplex
    Posts
    4,910
    Post Likes
    I hear ya Lusker, but if I did that I'd have to reinvent the wheel as there is a sharp 90 about 8' above the one in the pick.

    The system in question was rated at 15.0 amp MOP and some knucklehead ran 8 ga solid to the outdoor disconnect.

    Here's what I did - and I hope it works ok long term.

    I didn't have 12 in my truck, but had 10 stranded so I pulled the 3 8's and ran 10's. My thinking is the stranded wire will be a little less rigid in the conduit and the difference in wire size should allow more play room.

    What do ya think?

  4. #4
    Join Date
    May 2004
    Posts
    12,477
    Post Likes

  5. #5
    Join Date
    Jan 2006
    Location
    DFW Metroplex
    Posts
    4,910
    Post Likes
    Quote Originally Posted by Lusker View Post
    you know the wire size depends on the lenght of run too.. but...


    I hope you used rubber wire bushings or a wire clamp or both with a sevice loop in the box...


    I'll sic Bob on ya if not.
    Yeah - the run - it's about 40' from the panel......thought it, forgot to mention it

    Wires bushed and looped.

  6. #6
    Join Date
    Feb 2004
    Location
    Medford Oregon
    Posts
    807
    Post Likes
    3 main cause of breaker trip
    1. wire size
    2. bad contactor
    3 turn to turn shorts in motor windings
    there are others, but these are the main ones

    note: check of winding ohms to mfr spec will confirm if it's #3

  7. #7
    Join Date
    Jan 2006
    Location
    DFW Metroplex
    Posts
    4,910
    Post Likes
    Quote Originally Posted by rocket View Post
    3 main cause of breaker trip
    1. wire size
    2. bad contactor
    3 turn to turn shorts in motor windings
    there are others, but these are the main ones

    note: check of winding ohms to mfr spec will confirm if it's #3

    This one was a rub-through and short to ground, plain and simple.....but your reply is valid.

  8. #8
    Join Date
    Jan 2007
    Location
    maine
    Posts
    796
    Post Likes
    u should have any problems with cutting the insulation on those 90s.. They are pull 90's so just break them apart and feed the wire

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.
Comfortech365 Virtual Event