    The manual J of my home comes out essentially as a toss up between the 100,000 btu and 80,000 btu carrier infinity gas furnace-- house is 3 levels, 2700 square feet, located in washington dc built in 1930's. Other than storm windows and insulation in the attic, not very tight. Since the Infinity is a two stage unit, with the 100,000 btu model cycling down to 60,000 btus in low speed, does this make the decison less critical since it will be operating at 60,000 btus in milder weather? Am I off base thinking this way? Thanks
    Apr 2005
    new jersey
    Your furnace max BTU heat output should match your manuel J load. With the mild temps the low stage would run most often saving you fuel And then only on extreme temps both stages would operate.
    It's my understanding that low stage ,will not save fuel,just longer run times to help obtain more comfort.
    So,in this case the 80,000 btu furnace would give you more comfort.Can you add insulation,etc.,to it the corect size?
    What if you did the Man. J with a slightly cooler indoor design temp.,how much cooler would make it the correct size,and can you live wth that in extreme weather??
    Additionally ,the smaller furnace moves less air,which might be a big plus with older,possibly undersized ducts.
    Would the two speed function mitgate the issue more than a one speed furnace?
    Quote Originally Posted by ron3637 View Post
    Yes!
    PA/DE area
    Make sure if you go with smaller heater ,you have the cfm to drive a/c system
    It's NOT the BRAND,it's the company that installs it!!!!!
    So going with the 100,000 btu unit may benifit the ac functionality?
    Oct 2007
    STL Metro East
    The 100,000 btu and 80,000 btu carrier infinity gas furnaces are both available with 2,000 CFM blowers. The 80,000 btu model can be ordered as a 1,400 or 2,000 CFM model. According to Carrier, for a 4 ton or larger AC, you would need the 2,000 CFM model.
    So it makes no differnce if you go with the larger blower. But from what I take away here the 100.000 btu unit, since it has two speeds, would not likely be too oversized in any event. make any sense?
    The smaller furnace would be beter,if it would "cover" the heating load.
    Nov 2007
    Chicago
    If you are borderline, go with the bigger furnace. With two stages, the gas consumption on both will be negligible. The price difference between the two air handlers should also be negligible. Better to be safe and have a little bit too much heat than not enough.
    Infinity Gas Furnace Selection
    Quote Originally Posted by hvacconsultant View Post
    Thanks for your emphatic recommendation to GO WITH THE BIGGER FURNACE. There seems to be some confusion since other times you hear that in HVAC work, "bigger is not better". I listened to my dealer's advice and went with a smaller furnace last November and now he is delaying replacement with a 5 ton system (25HNA9 plus 58MVB100-20).
    Both my 4 ton hp and furnace have operated more than 45% in high stage. This made me suspect that they were undersized since the hp is supposed to run 80% of the time in low stage. Just when the high stage of the hp (48,000 BTU) has been reached, the 49,000 BTU low stage of the furnace can barely keep up and shifts into high stage (70,000 BTU) also. If I'm undersized, my furnace's 49,000 BTU low stage is virtually useless.
    I'm gambling that I would be using more of the 5 ton furnace's low stage (61,000 BTU) than it's 93,000 BTU high stage. Would be nice if Carrier had a medium stage of say 75,000 BTU for their 5 ton gas furnaces. Any thoughts.
    Jun 2001
    Louisville, KY
    I can't see doing 3 floors with one system. I'd be looking at multiple systems for that many levels.
    Heck, I'm zoning 3200 sf on 2 levels.