    Scotsman Icemaker Model CO630

    I have red blinking light and code 2 flashing. I reset but works and stop in harvest mode.

  2. #2
    Join Date
    Aug 2012
    Location
    willowick ,oh
    Posts
    261
    Need more info.

  3. #3
    Join Date
    Aug 2012
    Location
    willowick ,oh
    Posts
    261
    Does the machine produce and drop ice in harvest before it shuts down. How long does it take. How is the water level. is the unit clean.If it shuts down after it drops ice or during ,just clean the eyeballs.They are on either side below the ice grid.Take side panels off.A 2 flash i think is refrig,diagnostic.It will lockout during harvest if no ice is seen dropping by the eyes.I call them eyes. I forgot what they are actually called.&5% of the time, ice machines shut down due to in-sufficient maintenance

  4. #4
    Join Date
    Aug 2002
    Location
    Southold.calm
    Posts
    5,701
    Quote Originally Posted by levert22 View Post
    I have red blinking light and code 2 flashing. I reset but works and stop in harvest mode.
    http://www.scotsman-ice.com/docs/upl..._manual_AW.pdf

  5. #5
    Join Date
    Aug 2012
    Posts
    6
    I just cleaned the unit a month ago. It will get to harvest mode and operate in harvest maybe 3 minutes and unit will go into alarm mode. I just pulled the water level sensor, and the water temp sensor to clean. I just replaced the water filter also and the unit ran for two cycles and went back to code 2. I didn't see the eyeballs. This unit just have the curtain with a sensor telling the motherboard the ice dropped. I will look again for them. I received a bin full code once after a cycle but the bin is empty. I looked for the sensor in the bin but undetected. Water level is good. Should I run the cleaning solution through the system ?

  6. #6
    Join Date
    Jun 2012
    Posts
    116
    Yeah, a prodigy won't have bin eyes If it didn't doesn't drop ice within three minutes, i think it will lock out. If it is dropping, you have a bad curtain switch

  7. #7
    Join Date
    Aug 2012
    Posts
    6
    Ok, Thank you

  8. #8
    Join Date
    Jun 2012
    Posts
    116
    Is it harvesting within that three minute time?

  9. #9
    Join Date
    Jul 2012
    Location
    North west Arkansas
    Posts
    86
    The meaning of the code should be listed on the door, I can't remember what they are offhand. If the magnetic switch on the curtain was bad, I don't think it would even start a cycle, thinking the bin was full. Check the thickness of your ice, it may be too thick or freezing over to the sides of evap or even to ice probe itself.
    Check the bin switch by opening and closing the curtain while watching the light on the board.

  10. #10
    Join Date
    Jun 2012
    Posts
    116
    Quote Originally Posted by texasgentleman2 View Post
    The meaning of the code should be listed on the door, I can't remember what they are offhand. If the magnetic switch on the curtain was bad, I don't think it would even start a cycle, thinking the bin was full. Check the thickness of your ice, it may be too thick or freezing over to the sides of evap or even to ice probe itself.
    Check the bin switch by opening and closing the curtain while watching the light on the board.
    That would depend on if the switch failed open or closed...

  11. #11
    Join Date
    Jul 2012
    Location
    North west Arkansas
    Posts
    86
    Quote Originally Posted by danbb View Post
    That would depend on if the switch failed open or closed...
    True dat, that's why he should look for the light while manipulating the curtain.

  12. #12
    Join Date
    Jun 2012
    Posts
    116
    Quote Originally Posted by texasgentleman2 View Post
    True dat, that's why he should look for the light while manipulating the curtain.
    Yeah, I have this nagging feeling that this is a DIY though....

  13. #13
    Join Date
    Jul 2012
    Location
    North west Arkansas
    Posts
    86
    Yeah, I think so, everything they need to know is on the label on the door,,, in english,, The rest is just common sense.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event