    armstrong heat pump problem

    i am a service tech with a problem with a 12yr old armstrong heat pump the condesor coil freezes up from time to time gauge presures are l=25 h = 315 could it be the expansion valves if so wich one is bad condesor or evaprator ive changed the defrost bd thinking this may be the problem mostly in the past i worked on orfice systems not txv.
    Last edited by discount; 12-09-2007 at 10:52 AM.

  2. #2
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    33,902
    Sorry, you've come to the wrong place for DIY help. Need to find someone qualified to be working on a heat pump.

  3. #3
    Defrost thermostat.

  4. #4
    Join Date
    Jun 2007
    Location
    Round Rock
    Posts
    3,518
    Sounds like a restriction somewhere. Could be bad metering device or trash floating around in the system.

  5. #5
    Join Date
    Jan 2007
    Location
    Granger, IN
    Posts
    49
    i am surprised your 12 year old armstrong was installed with TXV.

  6. #6
    Join Date
    Mar 2007
    Location
    Quebec, Canada
    Posts
    56
    I'm also surprised that a service tech doesn't know which tx valve to check. NO DIY.

  7. #7
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,741
    What would you check, if it was a piston metering device.

    Picture the refrigerant systems flow in your mind.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?