    Why does freezers use a LL solenoid / pump down to kill the compressor
    via a low pressure switch rather than simply put the t-stat in series with the coil ?
    I know there is a logical reason.
    td55

  2. #2
    Join Date
    Jul 2012
    Location
    Everett, WA
    Posts
    270
    Post Likes
    To keep a solid colmun of liquid to the TXV

    Sent from my SCH-I915 using Tapatalk

  3. #3
    Join Date
    Sep 2007
    Location
    NH
    Posts
    1,424
    Post Likes
    Main reasons would be to prevent liquid migration and prevent flood back on start.

    Sent from my SM-G900V using Tapatalk

  4. #4
    Join Date
    Sep 2007
    Location
    NH
    Posts
    1,424
    Post Likes
    Most low temp pumps also don't like starting with a high suction pressure.


    Sent from my SM-G900V using Tapatalk

  5. #5
    Join Date
    Mar 2014
    Posts
    460
    Post Likes
    Quote Originally Posted by caheiman30 View Post
    To keep a solid colmun of liquid to the TXV

    Sent from my SCH-I915 using Tapatalk
    WRONG! it prevents refrigerant from leaking out of the evaporator during the off cycle or defrost

    Sent from my Nexus 5 using Tapatalk

  6. #6
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  7. #7
    Join Date
    Jan 2014
    Posts
    2
    Post Likes
    tanx

  8. #8
    Join Date
    Jun 2002
    Location
    nw ohio
    Posts
    257
    Post Likes
    many lo temp compressors are murdered due to flood back from the evaporator after defrost.
    pump down prior to defrost can also speed up defrost time.
    "Compressors never die; they're always murdered!" - Glenn Hannegan Jr

  9. #9
    Join Date
    May 2008
    Location
    Meridian, MS
    Posts
    419
    Post Likes
    Thread Starter
    I see. When you say "flood back from the evaporator", are you saying that without a LL solenoid, in the off cycle, as a system equalizes, liquid from the condenser migrates to the evap? And then upon start up, the compressor is somewhat flooded? Does this not happen in every system without a solenoid? somewhat?
    td55

  10. #10
    Join Date
    Oct 2008
    Location
    In a kitchen with my head stuck in an oven
    Posts
    1,659
    Post Likes
    What was said...AND fewer wires from the W/I box to the roof. Plus - lighter load for compressor to start up. Yes...floodback, especially in low-temp (freezer) units.

  11. #11
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    Quote Originally Posted by tonydykes55 View Post
    I see. When you say "flood back from the evaporator", are you saying that without a LL solenoid, in the off cycle, as a system equalizes, liquid from the condenser migrates to the evap? And then upon start up, the compressor is somewhat flooded? Does this not happen in every system without a solenoid? somewhat?
    A freezer, be it a walk in or self contained has additional "safeties" so to speak to help prevent slugging or overloading the compressor. Fan delays, accumulators, pressure limiting powerheads on the txv's, and cpr valves all help lessen the effects.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  12. #12
    Join Date
    May 2000
    Location
    Monmouth Junction-NJ-USA
    Posts
    6,125
    Post Likes
    Quote Originally Posted by tonydykes55 View Post
    I see. When you say "flood back from the evaporator", are you saying that without a LL solenoid, in the off cycle, as a system equalizes, liquid from the condenser migrates to the evap? And then upon start up, the compressor is somewhat flooded? Does this not happen in every system without a solenoid? somewhat?


    Refrigerant will always migrate to the coldest area of the system.
    If you really know how it works, you have an execellent chance of fixin' er up!

    Tomorrow is promised to no one...

  13. #13
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    Quote Originally Posted by tonydykes55 View Post
    I see. When you say "flood back from the evaporator", are you saying that without a LL solenoid, in the off cycle, as a system equalizes, liquid from the condenser migrates to the evap? And then upon start up, the compressor is somewhat flooded? Does this not happen in every system without a solenoid? somewhat?
    In addition to what rayr said
    Migration is to the coldest spot in the system. Without a LL solenoid and proper low ambient controls the compressor may never come on and/or never cool properly in areas where the outdoor ambient is lower than the box temperature. I know of a few R12 coolers in Chicago that worked with no llsv thru many winters. They may have worked just ok because of the pressure to temperature relationship. Won't work with the refrigerants that have come into the picture since then.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  14. #14
    Join Date
    Sep 2013
    Location
    Florida
    Posts
    423
    Post Likes
    I have several walk in coolers where the pump is either wired in series with the stat or with a LPC that controls temp. When satisfied, they simply cycle the pump. Been like that for years. But the condensers are located inside with little change in temp.
    I have not seen any freezers this way though.

  15. #15
    Join Date
    May 2008
    Location
    Meridian, MS
    Posts
    419
    Post Likes
    Thread Starter
    I understand. So then, in an typical residential split system for example, would I be correct in thinking that since the indoor ambient is typically 68 -74 degress, for example, there is not as much migration as in a 0 degree freezer - therefore no need for a solenoid/pump down? Did I say that right? And the fact that they
    are not low pressure systems? Another question: is the defrost termination for the evap fans - strictly to keep from circulating warm air?
    td55

  16. #16
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    Circulating warm air would be the last reason for the fan delay. The main purpose of the defrost termination/fan delay is to lower the load on the compressor at the end of the defrost cycle. It's also used to allow the moisture that has formed on the coil and hasn't dripped into the drain pan during the defrost cycle to freeze, preventing the moisture from blowing out of the coil and forming water droplets on the ceiling in front of the coil.(water droplets can form in other areas for other reasons) Some controls allow you to set for drip time.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  17. #17
    Join Date
    May 2008
    Location
    Meridian, MS
    Posts
    419
    Post Likes
    Thread Starter
    thanks, this has been very educational.
    td55

  18. #18
    Join Date
    Oct 2009
    Location
    Raleigh, NC
    Posts
    1,022
    Post Likes
    I have heard many times that the main purpose of a fan delay is to lower load on compressors. I don't really agree.

    During hot pull down, the fans stay off until coil is below freezing, then they come on and the coil is very quickly very warm from the warm box. In essence, it did reduce the load, but only for a short time.

    During defrost recovery in walk-in's, the fans running would actually help reduce load on compressors due to cold box air being pulled over coil.

  19. #19
    Join Date
    Sep 2013
    Location
    Florida
    Posts
    423
    Post Likes
    I think the main reason for a defrost termination would be to eliminate defrost if not needed. A typical defrost schedule is set for 40 mins. 4 times a day. On a busy day when the door is open often allowing in humidity and running constantly trying to keep up. It may need 40 mins. to defrost. Which is automatically controlled by the timer to terminate. But when the door is not being opened, like over night, days off, ect. Once the food and the box is at temp, its not working that hard to keep it there. So it may only take 5 or 10 mins. to defrost. At this point the defrost terminator will terminate defrost and cycle the compressor back into cooling. Most are rated for 55 degrees and mounted on the coil or end plate. Coming out of defrost the coil will still have water on it. As mentioned by 2sac. Some will allow for drip time, controlled by the timer. And some will bring the compressor on right away, which will freeze whatever is left before allowing the fans to run. Most are rated for 20 degrees to activate the fans, also mounted on the coil or end plate. I think the main reason for this is to prevent the box from turning into an igloo. Water would be thrown everywhere without using fan delays.

  20. #20
    Join Date
    May 2000
    Location
    Monmouth Junction-NJ-USA
    Posts
    6,125
    Post Likes
    Quote Originally Posted by MicahWes View Post
    I have heard many times that the main purpose of a fan delay is to lower load on compressors. I don't really agree.

    During hot pull down, the fans stay off until coil is below freezing, then they come on and the coil is very quickly very warm from the warm box. In essence, it did reduce the load, but only for a short time.

    During defrost recovery in walk-in's, the fans running would actually help reduce load on compressors due to cold box air being pulled over coil.
    Stay away from whoever told you that reasoning. Many systems have a CPR (crank case regulator) on them to keep the load low on the compressor when new start up or coming out of defrost.
    If you really know how it works, you have an execellent chance of fixin' er up!

    Tomorrow is promised to no one...

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •