    Do any of you market guys have the case load (Btuh/Door) and evap temp for this case? for both FF and ice cream? (I assume from the model number this is an ice cream case, but it'll be used for frozen food.)

    My Hussmann data doesn't cover that one.

  2. #2
    Join Date
    Sep 2005
    Location
    florida
    Posts
    5,524
    Post Likes
    Quote Originally Posted by icemeister View Post
    Do any of you market guys have the case load (Btuh/Door) and evap temp for this case? for both FF and ice cream? (I assume from the model number this is an ice cream case, but it'll be used for frozen food.)

    My Hussmann data doesn't cover that one.
    Sorry ice I couldnt fine any info on it.
    I love the smell of phosgene first thing in the morning:

    To apply for professional membership click here


    Educational forums are open.

    If you would like to submit a link or an article or other related info to the EF. click here

  3. #3
    Join Date
    Jun 2005
    Location
    Las Vegas NV
    Posts
    1,199
    Post Likes
    Same here ice, My books don't list that model. Hussmann want help anymore either, which I'm sure you know.

  4. #4
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    13,071
    Post Likes
    Thread Starter
    Quote Originally Posted by powell View Post
    Same here ice, My books don't list that model. Hussmann want help anymore either, which I'm sure you know.
    Yes I know....Those Bass-Turds.

    ...and to think that my father, who was a Hussmann distributor back in the 1950's into the mid 1970's, was personal friends with the then president of Hussmann (Gordon Gary ?) who also retired to Vero Beach.

    If Pop were still around, I'd have that info in a heartbeat.

  5. #5
    Join Date
    Oct 2007
    Location
    The rainy state
    Posts
    172
    Post Likes
    the magical # you are looking for is 1650 btu's per door. pulled this from a set of prints on a job a few years back on some NRCV's which are the same as NRC5L, your fronts are lower.

  6. #6
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    13,071
    Post Likes
    Thread Starter
    Quote Originally Posted by chilly123 View Post
    the magical # you are looking for is 1650 btu's per door. pulled this from a set of prints on a job a few years back on some NRCV's which are the same as NRC5L, your fronts are lower.
    Thanks chilly.

    You didn't happen to note what the evap temp was on those did you?

    Was that job a parallel rack system or conventional singles? The Btuh/Door rating is usually about 10% higher for singles, which is what I'm going to be dealing with.

  7. #7
    Join Date
    Oct 2007
    Location
    The rainy state
    Posts
    172
    Post Likes
    that would be -19. this was a parallel rack, for conventional unit use 1750 btu's. the loads are the same as the same as the classic line RFA. I still have the case cuts on these.

  8. #8
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    13,071
    Post Likes
    Thread Starter
    Thanks again!

  9. #9
    Join Date
    Jun 2005
    Location
    Las Vegas NV
    Posts
    1,199
    Post Likes
    Quote Originally Posted by icemeister View Post
    Was that job a parallel rack system or conventional singles? The Btuh/Door rating is usually about 10% higher for singles, which is what I'm going to be dealing with.
    You know, I've always questioned this rack vs. single system btuh rating for supermarket type equipment. If the btuh is 1650 for rack, why is it 1750 for a single? A btuh is a btuh. Is it because the ambient conditions change and a single loses capacity? If so, then is it really 1750 that is required and the rack system can adjust for this.

    What am I missing?

  10. #10
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    13,071
    Post Likes
    Thread Starter

    Conventional Unit vs. Parallel System Capacities...

    Quote Originally Posted by powell View Post
    You know, I've always questioned this rack vs. single system btuh rating for supermarket type equipment. If the btuh is 1650 for rack, why is it 1750 for a single? A btuh is a btuh. Is it because the ambient conditions change and a single loses capacity? If so, then is it really 1750 that is required and the rack system can adjust for this.

    What am I missing?
    It has to to with what Hussmann called system "diversity" in parallel, or what they called them, "mixed multiplexed" rack systems.

    Here's their explanation of diversity taken from the Hussmann New System Planning Manual from 1976:

    Conventional Units Versus Mixed Multiplexing Capacities

    "There is a basic difference between the actual capacity of a conventional unit must have for a particular case versus a mixed multiplexed unit operating the same case. When the conventional unit is applied, the unit must handle the case balanced load, pulldown load after defrost, along with a cycling ability to maintain temperature in the case with a pressure control or thermostat. When the same refrigerator becomes a part of a total load on mixed multiplexing, there is a certain diversity that the unit can handle due to normal defrosts, load variations, etc. on the system. Because of this diversity the capacity for the case can be applied without the pulldown, cycling requirement."

    So in a nutshell Powell, yes...a Btu is still a Btu, but the published case load ratings for the parallel racks are the "actual" or steady state BTU load for that case whereas the BTU ratings for the cases applied with conventional units have been kicked up a notch to account for the post defrost and cycling loads.

  11. #11
    Join Date
    Feb 2003
    Posts
    1,172
    Post Likes
    I concur with chilly on the btuh/door, most older CRH, RCA, NRC are approx, the same BTUH 1650/door on FF. (-5 F discharge temp required for FF -12 for ice cream)

    What refrigerant are the cases rated for as per nameplate??
    What are they running on?
    Have all required mods been made?

    What is the specific problem??
    Watts New, Ohm My, I been Electrically Commutated. Are U2.

  12. #12
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    13,071
    Post Likes
    Thread Starter
    Quote Originally Posted by mccool View Post
    I concur with chilly on the btuh/door, most older CRH, RCA, NRC are approx, the same BTUH 1650/door on FF. (-5 F discharge temp required for FF -12 for ice cream)

    What refrigerant are the cases rated for as per nameplate??
    What are they running on?
    Have all required mods been made?

    What is the specific problem??
    Thanks. No problems...yet.

    My customer bought 10 doors of "remanufactured" Hussmann NRC and 24 ft of Hill/Phoenix OHPH with conventional condensing units for each. I just saw the cases briefly the other day when I was at the store to cut loose and wave bye-bye to 24 ft of "ancient" WIZ wide island FF.

    The units didn't get delivered until yesterday. I just want to see what this reman outfit gives us for compressors and how they match up. The customer bought those H/P OHPH cases as multideck meat cases. I told them that the OHPH is a produce case.

    The fun is just beginning.

  13. #13
    Join Date
    Jun 2005
    Location
    Las Vegas NV
    Posts
    1,199
    Post Likes
    Quote Originally Posted by icemeister View Post
    So in a nutshell Powell, yes...a Btu is still a Btu, but the published case load ratings for the parallel racks are the "actual" or steady state BTU load for that case whereas the BTU ratings for the cases applied with conventional units have been kicked up a notch to account for the post defrost and cycling loads.
    icemeister,

    "Steady" was the thought process I was pondering.

    Thanks..........I'm mo smarter now.