Results 1 to 7 of 7
    Jul 2002
    Trane RTU Integration
    I will be bringing some Trane RTUs into Niagara this week. I am guessing they are reliatel. I have the LCI-I lit but can't find anything on what I'm guessing is LCI-R. Does anyone have that or the lit number? What about shadow object -vs- dynamic device? Seems like there are a lot of untitled SNVTs
    Nov 2005
    Shreveport, Louisiana
    post the model/serial and someone will tell you for sure if its Reliatel or not...
    Jul 2002
    Is there a way to get fan status? There is an alarm MUX which incorporates a dirty filter, fan failure, heat failure, but I need the status.
    Who would I contact, local office no help.
    Apr 2005
    Boulder,CO.
    If it's an LCI-I yes
    if it's an LCI-R, only if options module is installed w/fan switch
    Jul 2002
    It has the Reliatel board, there is another board in the blower section. There are DP switches on the filter and fan. When I link to the shadow object there is no fan status.
    I am having trouble linking the Niagara setpoints to any shadow object inputs.
    Apr 2005
    Boulder,CO.
    I'm showing NVO FAN SPEED it reports 0% OR 100% it's supposed to be the fan staus output according to Install Guide ACC-SVN19B-EN
    NY