    let me throw a few facts out at you about this machine

    for it to go off on "harvest to long" fault it has to be in harvest 3 times in a row taking more then 3 and a hafe mins each time.
    the water prob will put the machine into harvest after it is grounded out via water for 7 seconds.
    now step back and think for a second
    supply water problem no " set your head pressure back where is was"
    thats for sure not your problem.
    have a look for this..

    first one is bad ice thickness prob, if you do replace it replace it with the "T" one.. there is a kit

    second one i have seen in these machines is the horizontal's on the
    evapartor come lose and the ice doesnt drop properly

    also on these machines the lines on the back of the evaprator will let go from the evaprator.

    the dump valve might be stuck open a little bit causeing the ice to just fourm on the top of the evaprator and not drop because there is no weight and go back into harvest after the 3 and hafe mins..

    to make sure it isnt the charge or the lines letting go off the back of the evaprator unplug the water pump and turn it on if your evaprator inlet and out let don't freeze you may be low on gas.... a good rule of thumb is if your evaprator doesnt completly freeze over with no water running your low on gas, if it does dont touch your charge. when i do this i like to pull the evaprator splash gaurd off and put a magnet on the sencer so i can watch it frezze and see if there is any irregularities in teh freezing pattern. if there is you may wanna.............

    i could go on all night just have a look at that stuff for now.
    Last edited by desroches; 12-05-2007 at 10:00 PM.

  2. #22
    Join Date
    Mar 2003
    Location
    haciendia heights
    Posts
    146
    Post Likes

    Talking

    could be bad regulator or wasent set right 300 should get it done i have had lots of manis remote that i have put fan controls and run 315/260

  3. #23
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,815
    Post Likes
    Quote Originally Posted by desroches View Post
    let me throw a few facts out at you about this machine

    when i do this i like to pull the evaprator splash gaurd off and put a magnet on the sencer so i can watch it frezze and see if there is any irregularities in teh freezing pattern. if there is you may wanna.............

    i could go on all night just have a look at that stuff for now.
    If your arm gets tired holding a magnet on the switch just remove the water curtian and it will stay in freeze - no extra magnet needed-

    PHM Unit is 220 V. Is there a ground wire pulled from the panel or is it just case grounded? Are the water pipes copper or plastic? With the new water filter you may have lost a ground from the water pipe.
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  4. #24
    Join Date
    Mar 2005
    Location
    Fort McMurray, AB
    Posts
    113
    Post Likes
    With the new water filter you may have lost a ground from the water pipe.
    never even caught that, i am impressed !


    *clapps !*

    oh wait but the water itself is grounded.

    the ground from the board to the unit should be the only one that matters

    bad netural though could mess up the board with the unit still running

  5. #25
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,815
    Post Likes
    Quote Originally Posted by Poodle Head Mikey View Post
    Last Thursday I was there and the unit was off on "excess harvest time". It's is spotlessly clean inside but did take it's time dropping ice - more than two minutes. I sprayed the cube molds with silicone and it then dropped the ice Very soon into defrost.

    Is there anything else I can do to speed up the ice dropping?

    Any ideas?
    If all you did was slick up the evap plate and the ice dropped fine the plate is dirty or plating is trashed. Remove the water curtain while in freeze just before harvest. Let cycle into harvest with out water curtian on and let the ice drop. Then let the unit run the full 3.5 min with curtain off. The machine will cycle off(full bin).The plate will begin to dry up and you will see the crud. If it is white lime you can clean with I/M cleaner and nylon brush. If the deposits are red iron Good Luck getting it off without destroying the plating.
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  6. #26
    Join Date
    Mar 2005
    Location
    Fort McMurray, AB
    Posts
    113
    Post Likes
    also i think that its should produce a sheet of ice every 18 to 20 mins and drop that sheet in at least 3.5 mins

  7. #27
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,815
    Post Likes
    Quote Originally Posted by desroches View Post
    never even caught that, i am impressed !


    *clapps !*

    oh wait but the water itself is grounded.

    the ground from the board to the unit should be the only one that matters

    bad netural though could mess up the board with the unit still running
    If the water line is plastic - no good ground through water.
    If new water filter is all plastic lost the poor ground he had.
    Ground though a water pipe or elec. pipe case is a bad idea.
    Need good ground to panel not just the little wire from the board to the frame.
    Machine needs a consistent ground. If ground is loose or is changing it messes with the board.
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  8. #28
    Join Date
    Mar 2005
    Location
    Fort McMurray, AB
    Posts
    113
    Post Likes

    Talking

    yeh i agree, air bubbles in the water line may cause issues, also the water psi was jacked up he said, so this could kinda backup air bubbles making the ground not so good all the time.

    this is fun

  9. #29
    Join Date
    Sep 2001
    Location
    Rochester, New York
    Posts
    1,385
    Post Likes
    Not sure if you found the problem yet, but my vote is the dump valve.

    My guess is that it is not opening, and the water gets so mineral ladent that it will no longer freeze.

    Just a guess.

  10. #30
    Join Date
    Apr 2007
    Location
    Loris SC
    Posts
    208
    Post Likes

    ???????

    This is why they changed the Q-Model and the S-model's Harvest failare safety to 3 times to 500 times

  11. #31
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,825
    Post Likes
    Thread Starter

    No news - is that good news ?

    Either that or I have been fired I guess. <g>

    I think the water sump being empty thing is incidental to the unit locking off on "long harvest time safety". The unit just goes off when the sump is empty. The empty sump is just another bit of meaningless data.

    Last time there the discharge line was barely into the 160's. I raised the head pressure to get it over 170. So far as I can remember - that's all I changed. So far - no further word. I gave all the bar girls my cell number and instructions to call me at any time so I'm thinking I would have heard if there was no ice. <g>
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  12. #32
    Join Date
    Jan 2007
    Location
    maine
    Posts
    796
    Post Likes
    Quote Originally Posted by itsiceman View Post
    If the water line is plastic - no good ground through water.
    If new water filter is all plastic lost the poor ground he had.
    Ground though a water pipe or elec. pipe case is a bad idea.
    Need good ground to panel not just the little wire from the board to the frame.
    Machine needs a consistent ground. If ground is loose or is changing it messes with the board.
    i agree.. A bad ground to the unit will play with the board and make it do all kinds of things, just like loose common wires will.. Poodle head mikey, if it was me id tell the bar when it locks out to LEAVE it alone so u can show up and see whats up with this thing.. there nothing worst then trying to find a problem in a unit when it works perfect when you r there.. Tell them to steal ice from another machine and just fill the bin manually .. Most manis recommend 150 degree discharge temp or greater.. manitowoc said they went from 3 cycles to 500 before locking out because of many nusense calls.. I just left one of there seminars today

  13. #33
    Join Date
    Dec 2007
    Posts
    614
    Post Likes
    [QUOTE=Poodle Head Mikey;1692385]It is a country club. This particular ice machine is in the pro-shop bar.

    could you be missing the big pic?maybe in the evening when the sprinklers kick on to water the greens there is a major pressure drop and now the greens don't need so much water then no calls?just a thought

  14. #34
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,825
    Post Likes
    Thread Starter

    The greens have their own well -

    The clubhouse, catering, bars, and pro shop are the only things using this well. My thinking has been that if the pressure was going to drop - it would happen when the buildings were in use during the day and not when they were all closed for business.

    I've already raised their pump / tank pressure.

    And I do not believe that they are running the machine without water anyway. Why would that stop the machine on long harvest? And even if it did - how could it possibly happen before tripping the high pressure cut-out? And I would know because it is manual reset.

    Raising the head pressure / discharge line temperature has either solved the problem - or they have gotten someone else. Because I haven't heard from them. <g>
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

+ Reply to Thread
Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •