    A Mystery Manitowoc -

    This is a Q unit, maybe 600 lb. Water-cooled head, ten years old.

    The operators say: we find it not running in the morning. Bine is not full. We switch it off. We fill it with water from a pitcher. We turn it back on and it runs fine - making ice.

    It's on well water. Recently I have replaced the clogged water inlet valve, installed new water filters and rack, and installed a 10 micron pre-filter for well sediment.

    The condenser water is unfiltered but the head pressure is always normal. And I have never found it off on the manual-reset HP control.

    In the summer they had water pressure problems when lots of people were flushing toilets. But now it is winter, the bar is very slow, hardly anyone uses the toilets, the pressure is steady, and I increased their well pump pressure from 45 to 60 lbs. besides.

    Last Thursday I was there and the unit was off on "excess harvest time". It's is spotlessly clean inside but did take it's time dropping ice - more than two minutes. I sprayed the cube molds with silicone and it then dropped the ice Very soon into defrost.

    Is there anything else I can do to speed up the ice dropping?

    Turning the switch off and then back on resets any board faults. But I just got off the phone with the manager and she claims that simply turning it off and then on agan does not refil or restart the machine.

    They say they can only make it re-start to make ice by adding water to the sump by hand.

    That makes no sense to me. As I understand it; the control board's water fill function works solely based on power to the machine and the water level sensor - when the level falls: the water valve opens. When the water level touches the sensor: the water valve closes.

    What the hell can filling the sump from a pitcher have to do with that?

    Any ideas?
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  2. #2
    Join Date
    Jan 2007
    Location
    maine
    Posts
    796
    Post Likes
    in my experience take what people have to say with a grain of salt...They will tell u what they want.. Personally i would pull the charge and weight it back in with new gas just to eliminate that aspect of it.. then see if the issue resumes

  3. #3
    Join Date
    Apr 2005
    Location
    where the beer flows like wine
    Posts
    2,869
    Post Likes
    it needs a new board and I have one for sale

    http://hvac-talk.com/vbb/showthread.php?t=155437

  4. #4
    Join Date
    Nov 2007
    Location
    State College, Pa.
    Posts
    42
    Post Likes
    check the dump valve, may be partly open, also check the water regulator on the condenser, low head pressure will cause long harvest times, as well as hpr valve.

  5. #5
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,749
    Post Likes
    Recheck the level of the machine. I had a customer redo some tiles in the kitchen and knocked the unit out of level. Water would hit the sump level probe every now and then and it would never refill. When enough frost built on the plate the curtain wouldn’t open. 3 or 4 times I had to go back.

  6. #6
    Join Date
    Jan 2007
    Location
    maine
    Posts
    796
    Post Likes
    Any one have that manitowoc bulliten about the new thumb screw.. maby the machine thinks the water tray is full and its not but when they pour water in and turn back on she goes to town i will search for it i dont remember the models affected.. sorry thats the s model machines just found it
    Last edited by yotaman16; 12-03-2007 at 06:47 PM.

  7. #7
    Join Date
    Mar 2007
    Location
    Toronto
    Posts
    264
    Post Likes
    I have had three Manitowocs where the water fill light was constantly on as long as any wire longer than three inches was attached to the probe connection. The cheapest solution was to install a float valve as the PC cards are very expensive here. This would account for the sump fill solution by the customer.
    An erratic board is not a rarity.

  8. #8
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,828
    Post Likes
    Thread Starter

    Doctor Ice -

    On this unit the fill function and full light appear to work perfectly - when I am there.

    If I short the probe to ground - the light comes on and the fill valve closes. If I take the jumper off - the light goes out and the fill valve opens.

    Then when the water leverl comes up to touch the probe - the light comes on and the fill valve closes.

    Just like clock work.

    A few days later they call me with the same story as before.
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  9. #9
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,817
    Post Likes
    Still banging your head with this one A bad toggle (or loose ground) switch can give you all kinds of erratic symptoms I found one by wiggling the wiring in the control panel. The toggle had a bad connection and would act up instantly (but I missed it for something else previously). Also for the times with no error code stored have you noticed if the front cover has an indentation around the toggle switch area. Some older ones would turn themselves off if the front cover was bumped ( The cover plastic was smooth )
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  10. #10
    Join Date
    Nov 2007
    Location
    State College, Pa.
    Posts
    42
    Post Likes
    Quote Originally Posted by fuzzyj View Post
    check the dump valve, may be partly open, also check the water regulator on the condenser, low head pressure will cause long harvest times, as well as hpr valve.
    pecmsg is right, after thinking further about this, your problem is strictly water related. As pecmsg states, no water or little water in the sump= a small amount of ice on the evaporator, not enough to move the curtain during harvest, harvest times out, instead of resetting by way of the curtain x 10 = extended harvest trouble code.

  11. #11
    Join Date
    Sep 2007
    Location
    Balto, MD.
    Posts
    199
    Post Likes
    Quote Originally Posted by pecmsg View Post
    Recheck the level of the machine. I had a customer redo some tiles in the kitchen and knocked the unit out of level. Water would hit the sump level probe every now and then and it would never refill. When enough frost built on the plate the curtain wouldn’t open. 3 or 4 times I had to go back.
    I've had this happen to me also, now it's something I check often. I often tilt the level slightly forward to help with the ice harvest. A trick I learned from a older tech on a old worn out Scottsman.

  12. #12
    Join Date
    Mar 2003
    Location
    haciendia heights
    Posts
    146
    Post Likes

    Talking

    the code was long harvest at night water to cond colder lower head less hot gas to melt ice off of plate need to raise head pressure to get suctionto at least 90 psi

  13. #13
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,828
    Post Likes
    Thread Starter

    Bob 1420 -

    That ocurred to me yesterday. Although the discharge line was above 160 I thought the same thing. So I raised the head pressure to 300 lbs.

    And, as the run is long to get fresh well water, I thought that maybe each time I get to see the machine it is using "pipe water" which is warmer, rather than "well water" which is colder.

    Then, after a while, I leave, the well water shows up, the water temp is less, and the head pressure lower.

    But wouldn't the cond. water valve compensate for that? Controling the head pressure at the valve's set-point?
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  14. #14
    Join Date
    Dec 2007
    Location
    New York
    Posts
    23
    Post Likes
    Call the Manufactures rep.

  15. #15
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,828
    Post Likes
    Thread Starter

    Flare Nut -

    I did call them.

    They helpfully suggested that I re-read the manuals.
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  16. #16
    Join Date
    Dec 2007
    Location
    New York
    Posts
    23
    Post Likes
    I'm pretty good at this stuff. Later to day I'll try to resolve your problem. The office is very busy right now . I'll get back to you.

    Syd
    L&L Mechanical Services, Inc.

  17. #17
    Join Date
    Dec 2007
    Location
    New York
    Posts
    23
    Post Likes
    Just a few thoughts. Is the water source being interrupted during the night? Could someone have decided to shut or divert a water source during the evening hours such as the building laundry? Does the high pressure switch have a manual reset button on it?

    Syd

  18. #18
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,828
    Post Likes
    Thread Starter

    Flare Nut -

    It is a country club. This particular ice machine is in the pro-shop bar.

    the apparent pattern is that the machine stops harvesting quick enough sometime during the night and locks out on that fault.

    There would be no water use past say 10:00P. All the other ice machines are air-cooled.

    The high pressure control is manual reset. I have stopped them from automatically pushing it. The machine is clearly locking out on "excess harvest time".

    I had intended to go over there today and pitch the machine forward an inch and a half but I was out late exploding a steam boiler until ten last night and this morning hassling with Goodman, Johnstone, Amana, and a few no cooling refrigeration calls.

    I am headed out now to remedy a 95% Coleman furnace. So my spare time was somewhat limited today.

    All ice machine thoughts and suggestions welcome -
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  19. #19
    Join Date
    Mar 2007
    Location
    Toronto
    Posts
    264
    Post Likes
    Other than a bum board or water level sensor the only other thing I can think of is low water pressure at night where the sump doesn't fill fast enough and the water fill is cut off after 5 minutes. So enough water to cool but not enough to fill the sump in time.

  20. #20
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,817
    Post Likes
    I'm not saying it's the board but if you decide to change it the new one will not lock out on a nuisance #2 safety. Did you do any of the diagnosis chart?
    “If You Can Dodge A Wrench You Can Dodge A Ball”

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •