    "A" coil positioning on air handler

    Name:  ImageUploadedByTapatalk1399299588.307285.jpg
Views: 363
Size:  299.6 KBName:  ImageUploadedByTapatalk1399299608.706602.jpg
Views: 368
Size:  241.0 KB

    Here goes my first problem I ever discuss here.. Well I have a right handed air handler, the unit is freezing up but when I open the doors I notice the coil was backwards I just don't have install manual to confirm but I know it is . I'm I right or wrong or does it matter??


    Sent from my iPhone using Tapatalk

  2. #2
    Join Date
    Apr 2011
    Location
    SE Washington
    Posts
    707
    Post Likes
    it appears correct, the air in this pic would be entering the a coil at the right, exiting the left into supply

  3. #3
    Join Date
    Dec 2009
    Location
    Dallas-Fort Worth, Texas
    Posts
    90
    Post Likes
    Thread Starter
    Air is entering in left coming out in right.


    Sent from my iPhone using Tapatalk

  4. #4
    Join Date
    Dec 2009
    Location
    Dallas-Fort Worth, Texas
    Posts
    90
    Post Likes
    Thread Starter
    Supply is to right


    Sent from my iPhone using Tapatalk

  5. #5
    Join Date
    Feb 2011
    Location
    Peoria, IL
    Posts
    3,002
    Post Likes
    so this is a down flow?

  6. #6
    Join Date
    Dec 2009
    Location
    Dallas-Fort Worth, Texas
    Posts
    90
    Post Likes
    Thread Starter
    It's horizontal


    Sent from my iPhone using Tapatalk

  7. #7
    Join Date
    Dec 2009
    Location
    Dallas-Fort Worth, Texas
    Posts
    90
    Post Likes
    Thread Starter
    Horizontal right-hand


    Sent from my iPhone using Tapatalk

  8. #8
    Join Date
    Feb 2011
    Location
    Peoria, IL
    Posts
    3,002
    Post Likes
    i see that, but if supply come's out of bottom, its a down flow, if it comes out the top, its an up flow. Its on its side, so does it come out of the bottom, or top if you stood it up? (the supply)

  9. #9
    Join Date
    May 2004
    Location
    Salt Lake City/Tooele
    Posts
    9,679
    Post Likes
    How is the airflow and static? Looks to be a hungry 5 ton coil..need a lot of air to keep that beast fed, especially on a low ambient days if there is no head pressure or low-ambient controls.

    And coil is probably backwards,...I simply googled the install manual, see page 7
    Install manual is probably still sealed in a baggy along with all the accessory stuff in the blower compartment

    http://icpindexing.toddsit.com/docum...9601540202.pdf

  10. #10
    Join Date
    Nov 2011
    Location
    Phoenix,AZ
    Posts
    466
    Post Likes
    I think it's backwards all you do is change the location of the drain pan on those a bunch of air is probably bypassing the coil

  11. #11
    Join Date
    Dec 2009
    Location
    Dallas-Fort Worth, Texas
    Posts
    90
    Post Likes
    Thread Starter
    Thank you so much for the install manual! It is backwards and well the return has a plenum which is open at end to the ceiling. It has ceiling tiles and open grids as returns.


    Sent from my iPhone using Tapatalk

  12. #12
    Join Date
    Dec 2009
    Location
    Dallas-Fort Worth, Texas
    Posts
    90
    Post Likes
    Thread Starter
    I did try google but had no luck and it's in a commercial property that is just brand new!


    Sent from my iPhone using Tapatalk

  13. #13
    Join Date
    Feb 2011
    Location
    Peoria, IL
    Posts
    3,002
    Post Likes
    Coil is still backwards, meaning its going to hit the top plate of coil first, instead of going through the open a from the bottom as usual. (correct? im staying tuned because i have a system someone else installed, the same way, with issues)

  14. #14
    Join Date
    Dec 2009
    Location
    Dallas-Fort Worth, Texas
    Posts
    90
    Post Likes
    Thread Starter
    I did try google but had no luck and it's in a commercial property that is just brand new!


    Sent from my iPhone using Tapatalk

  15. #15
    Join Date
    Dec 2009
    Location
    Dallas-Fort Worth, Texas
    Posts
    90
    Post Likes
    Thread Starter
    Yes you are correct the bottom is freezing up and the top half is not


    Sent from my iPhone using Tapatalk

  16. #16
    Join Date
    May 2004
    Location
    Salt Lake City/Tooele
    Posts
    9,679
    Post Likes
    This stuff always happens in the worst working locations. Probably suspended in a location that is right in the path of every office employee who needs to get to the copy machine. I can work all day on rooftop units and still skip home, give me one suspended air-handler above a drop ceiling and I am sore for days.

  17. #17
    Join Date
    Feb 2011
    Location
    Peoria, IL
    Posts
    3,002
    Post Likes
    So if it hit's the top of a backwards coil (Airflow) and then choose's a slab of the coil with less resistance, and favors it, does that sound rite? If in the correct position, its forced into the a and airflow is better thru both slabs.

  18. #18
    Join Date
    Dec 2009
    Location
    Dallas-Fort Worth, Texas
    Posts
    90
    Post Likes
    Thread Starter
    Oh yeah! This is in a bank so I had to figure this out by 9am so I won't be in the way!


    Sent from my iPhone using Tapatalk

  19. #19
    Join Date
    May 2004
    Location
    Salt Lake City/Tooele
    Posts
    9,679
    Post Likes
    Quote Originally Posted by garychance View Post
    So if it hit's the top of a backwards coil (Airflow) and then choose's a slab of the coil with less resistance, and favors it, does that sound rite? If in the correct position, its forced into the a and airflow is better thru both slabs.
    I believe your on the right track...I think you can get away with having the top of an A coil in the path of the supply, like in certain down flow horizontal applications, but not in the path of the return.

  20. #20
    Join Date
    Feb 2013
    Location
    north georiga
    Posts
    2,998
    Post Likes
    is this typical of any a coil or just carrier (that is a carrier right?)

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •