    Fluctuating refrigerant pressures

    We were doing a start up on a Bryant A/C system that we installed today and after 5 minutes of running the low side was fluctuating between 110 to 125 psi and the high side was fluctuating between 250 to 290 psi. What could be causing this.

    Evaportator has a TXV
    Return 73
    Supply 55

    We have been installing Bryant for 5 years now and this is the first time that this has ever happened. The customer had to leave for a wedding today so I did not spend much time on diagnosing the problem.
    GET BENT HELMET!

  2. #2
    Join Date
    Jan 2014
    Location
    Mesa, Arizona
    Posts
    354
    Post Likes
    Was the system properly evacuated? Purge nitro while brazing? Vacuum to 500 microns? Purged hoses before adding 410a to compensate for lineset length? Is sensing bulb at evap insulated? Is entire lineset insulated?


    We all make choices, but in the end our choices make us.

  3. #3
    Join Date
    Jul 2009
    Location
    Damascus MD
    Posts
    6,160
    Post Likes
    Non condensibles, refrigerant wasnt added as 100% liquid, or txv hunting

    Sent from my SM-N900V using Tapatalk

  4. #4
    Join Date
    Sep 2005
    Location
    NJ
    Posts
    432
    Post Likes
    Thread Starter
    System was properly evacuated and purged while brazing.
    How do you test for non condensibles
    GET BENT HELMET!

  5. #5
    Join Date
    Jan 2013
    Location
    florida
    Posts
    1,405
    Post Likes
    is this 22 or 410 ?

  6. #6
    Join Date
    Sep 2005
    Location
    NJ
    Posts
    432
    Post Likes
    Thread Starter
    410
    GET BENT HELMET!

  7. #7
    Join Date
    Jul 2013
    Location
    Richmond, VA
    Posts
    6,027
    Post Likes
    If it's fluttering, it could be a blockage somewhere.

  8. #8
    Join Date
    Jun 2011
    Posts
    34
    Post Likes
    As always we need a little more info please. Does this unit have the new LG scroll compressor in it? What is your sub cooling and superheat? How fast does the head pressure change? How fast and how much is the sub cooling changing?

  9. #9
    Join Date
    Aug 2005
    Location
    Florida
    Posts
    375
    Post Likes
    I had to replace a locked up compressor on a rheem split a couple of years ago. Once I had the new compressor in and started it up, after a few miinutes of running it was doing the same thing. TXV was the culprit. New valve, and system was running fine.
    l8r

  10. #10
    Join Date
    Jul 2013
    Location
    McAllen
    Posts
    614
    Post Likes
    If you have done everything right look at your duct work. If it is under sized or if you can hear the air whooshing-fluctuating it could be bad or undersized duct work. Remember your txv reacts to temperature on suction line. Suction line temperature is based on evaporator coil temperature. If the air is fluctuating due to effective duct, so will your pressures.

  11. #11
    Join Date
    Jul 2013
    Location
    McAllen
    Posts
    614
    Post Likes
    I ment defective ducts. Sorry I'm using my phone

  12. #12
    Join Date
    Jul 2013
    Location
    McAllen
    Posts
    614
    Post Likes
    Terminology. Fluctuating or whooshing air is usually caused by a blower motor hunting for the right static pressure and air flow.

  13. #13
    Join Date
    May 2014
    Location
    New York
    Posts
    13
    Post Likes
    could be liquid sluggin that happened to me once and that's what it was but that was just once not really to sure though

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •