    Calculating BTU

    Hello,

    Has any one tried calculating BTU through DDC Logic? There is Temperatures sensor in the supply and return and a flow meter in the Chilled Water line. Any inputs on the best way to do it through programming in DDC logic and experience will be helpful.

  2. #2
    Join Date
    Jul 2008
    Location
    Melbourne
    Posts
    1,611
    Post Likes
    Quote Originally Posted by hmlhwl View Post
    Hello,

    Has any one tried calculating BTU through DDC Logic? There is Temperatures sensor in the supply and return and a flow meter in the Chilled Water line. Any inputs on the best way to do it through programming in DDC logic and experience will be helpful.
    Flow x Cp x td...more or less
    1 + 1 = 3 ( *** for very large values of 1)

    ...everybody wants a box of chocolates and long stemmed rose

    Be brave. You cannot get eaten by an imaginary tiger.

  3. #3
    Join Date
    Dec 2006
    Location
    What? Who? Where?
    Posts
    2,634
    Post Likes
    Accurate sensors (matched temperature).

    kontrol out
    "Good" - Jocko
    "Open is as open does." - Forrest Gump
    "Can't we all just get a Lon?" - Garry Jack
    "BACnet: integration or interrogation?" - The Janitor
    "Interoperability? You can't handle interoperability!" - Nathan R. Jessup
    “What’s that? Aaa… open protocols? Don’t talk about…. open protocols? Are you kidding me? Open protocols? I just hope we can hardwire an interface!” - Jim Mora Watch it here!

  4. #4
    Join Date
    Oct 2008
    Location
    Kalispell, MT
    Posts
    622
    Post Likes
    Quote Originally Posted by hmlhwl View Post
    Hello,

    Has any one tried calculating BTU through DDC Logic? There is Temperatures sensor in the supply and return and a flow meter in the Chilled Water line. Any inputs on the best way to do it through programming in DDC logic and experience will be helpful.
    There's a lot to doing that. Different control systems have different issues doing things like this. JCI for instance might not calculate the value in a known time frame. Depending on what is going on in the system and whether you are using a controller or LCT. Siemens can do it in a somewhat known time frame or you can force it to calculate at least every second. If you are not time sensitive I would use the El Goog and figure out what it would take for your system.

  5. #5
    Join Date
    Apr 2007
    Location
    San Diego, CA
    Posts
    2,254
    Post Likes

  6. #6
    Join Date
    Feb 2008
    Location
    Pacific Coast
    Posts
    201
    Post Likes
    $.02 :

    Calculations offered are for water. Glycol has different specific gravity, which affects the BTU calculation.

    I also tie a status point (flow / no flow) to stop the calculation to avoid value windup when not flowing.

    John

  7. #7
    Join Date
    Dec 2001
    Posts
    218
    Post Likes
    Wanna keep it simple try this product.

    http://www.onicon.com/?gclid=CKOg2snRkr4CFdDm7AodmSAAZA

    Rock solid reputation!

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •