Results 1 to 9 of 9
    Nov 2007
    Two cracked heat exchangers
    Hello
    I have the following situation:
    Summary:
    1. 3 level split house 1800 sq feet in the Seattle area
    2. In the last 8 two heat exchanger developed cracks .
    3. 8 years ago I have hired a local heating contractor to install a new gas furnace and got Carrier install. I don’t believe that salesperson did proper Manual-J sizing, but merely eye-balled the house, windows, etc to recommended proper sizing.
    The installed furnace is:
    Carrier 58RAV095, Input BTU 92000, 80% efficiency, therefore output BTU 74000.
    It may worth mentioning that during its 8 years inducer motor was replaced 3 times (two while previous inducer motor was on its own warranty)
    This is a second furnace with the crack, albeit a hairline crack.
    According to the rough estimate http://www.hvacopcost.com/equipsize.html the correct BTU for my house would be 79000. So the my furnace seems to be within the range.
    With all these said:
    1. Would what would cause 2 cracked heat exchangers in the course of 8 years? According to above reference furnace does not seem to be oversized
    2. Is there inherit problem with the Carrier 58RAV (keeping in mind 3 inducer motors which gone wrong)?
    The house is build in 1969, where there is no obstructions in the ducts, some rooms on the 3rd level have pretty poor airflow. I would attribute this to lack of proper design (too many 90 degree bends).
    Thanks,
    Apr 2004
    poor airflow, not changing filters, closed registers.... In otherwords, not getting the heat out of the HX.
    Nov 2007
    Hi
    I have electrastatic filters which are changed regulary. There are no closed registers.
    Is it possible to determine if airflow is bad or good? Can such determination be made by a heating company?
    First thing comes in mind is a measuring airflow speed in the plenum and comparing it with the furnace's recommended/nominal speed?
    Thank
    May 2005
    Western Kansas
    someone that knows anything about the trade should be able to take temperature and static pressure measurements and find the problem rather quickly. If you feel you aren't getting answers from this company, consider another after talking to friends and neighbors.
    SE Michigan
    Definatly an air flow issue either on return or supply or even both. Static pressure readings should be taken to find the problem. May be a venting issue as well.
    Can you post some photos?
    “Socialism is a philosophy of failure, the creed of ignorance, and the gospel of envy, its inherent virtue is the equal sharing of misery.”
    Jun 2001
    Louisville, KY
    Quote Originally Posted by LeonBrag View Post
    Do you really have an electrostatic filter, or do you have an electronic air cleaner?
    leland nc
    lack of combustion air can also be a factor with a cracked hx
    flame impingment from dust build up because of no servicing or not enough
    over fired because gas pressure wasnt checked
    air flo is a biggy
    there are many factors for a cracked hx that isnt near its life span
    a tech should be able to find the reason and retify it when the new furnace or hx is put back into service
    it is to late for the cracked one but not for the new one
    time to find the reason
    Nov 2007
    Sorry for the confusion, it's Electronic Air Cleaner 16x25. I had numerous techs from more then one company. None of them are interested in any real troubleshooting. They all propose:
    1. Change the furnace
    2. Change HX
    Is there a list I can give to the tech (or call heating contractors to perform checks), for example:
    1. Check static preasure
    2. Check termprature
    3. check if there is enough combasible air. Furnace is in the large crawlspace (tall enough to walk in), with only two crawlspace vents.
    Massachusetts
    For a problem like this, I'd do a telephone search and find a company that can and will do a professional Manual 'J' calculation. You'll have to pay for it but it's money well spent. Now that you've found the company that does it correctly, you can reasonably assume they'll work with you got try and resolve your problems. They should have the checklist but you've summarized it pretty well to start with.
    1. Temperature rise
    2. Total static pressure
    3. Gas pressure at the manifold with all gas appliances in operation
    It's most likely that with just these readings, a good tech can pin down the problem. I've seen recuperative coils plugged so badly that very little air can get past them. That will show up as a high temperature rise. So just find the right company I think your problems will be short lived.