    IBR Ratings

    After a heat loss is done, which BTU output rating is used? I have seen conflicting info on different websites, even from Weil-Mcclain themselves. Various people claim to use the I=B=R Rating others claim to use the DOE Rating, including Weil themselves.

    CGI - 6 Weil Boiler Specs Input - 167 MBH DOE Heating Capacity - 140 MBH Net I=B=R Water rating - 122 MBH If you us the IBR its an almost 20,000 btu difference, so which is correct???

  2. #2
    Join Date
    Mar 2007
    Location
    Myrtle Beach, SC
    Posts
    2,936
    Post Likes
    IBR rating allows for piping losses. On AC that is the same as duct gain and loss.

    When I was up north, we used IBR ratings.
    Remember, Air Conditioning begins with AIR.

  3. #3
    Join Date
    Jun 2007
    Location
    Minneapolis, MN
    Posts
    1,017
    Post Likes
    IBR is not as valid today as in the past as we now use smaller pipes, reset, lower water temperatures, etc. Still a good idea for cast iron boilers on old big pipe, high mass radiator systems.

    MA

  4. #4
    Join Date
    Jan 2004
    Location
    PA
    Posts
    75,879
    Post Likes
    Boiler location, and how and where the pipes are run determine if you need to use IBR, or DOE ratings.

    DOE rating calculates that all heat lost by the boiler through its insulation and jacket, plus any heat lost by the pipes heat the house.(like duct work in the conditioned space)

    IBR rating calculates all heat lost by both boiler and pipes is lost to the house(ducts in an unconditioned space)
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  5. #5
    Join Date
    Jun 2007
    Location
    Minneapolis, MN
    Posts
    1,017
    Post Likes
    I believe an unhealthy majority still us net IBR rating as THE sizing factor. This assumes that 15% of the net output of the boiler is lost before it gets to the conditioned space.

    If the pipes are in the conditioned space -still in the conditioned envelope- this heat is not lost. We could debate system efficiency - how fast the heat lost is replaced by the boiler - but the net heat output DOE is not lost.

    When you use IBR output - 15% too big by definition - then add the typical 10 to 20% "fudge" factor your customer gets over 25% more boiler than he needs. He will never know the difference but we should.

    MA

  6. #6
    Join Date
    Jul 2004
    Location
    Massachusetts
    Posts
    6,849
    Post Likes
    Much of the IBR factor is for a cold start application. It's call "Pick-up" and can account for up to 15% of the boiler capacity. It's really not accurate to say one method is better than the other because in some instances, IBR is a minimum need while in other instances even the DOE has a healthy margin. This is where it takes a true professional to determine which rating to use, IMO.
    If YOU want change, YOU have to first change.

    If you are waiting for the 'other guy' to change first, just remember, you're the 'other guy's' other guy. To continue to expect real change when you keep acting the same way as always, is folly. Won't happen. Real change will only happen when a majority of the people change the way they vote!

  7. #7
    Join Date
    Jun 2007
    Location
    Minneapolis, MN
    Posts
    1,017
    Post Likes
    A subtle observation. Were it that all our fellows were so astute.

    MA