Thread: 90+ gas furnace problems
-
11-22-2007, 11:06 PM #14
Regular Guest
- Join Date
- Oct 2007
- Location
- BC, Canada
- Posts
- 55
I have never seen a variable voltage ignitor? If you decrease the voltage and the resistance of the HSI remains the same, the amperage would increase. There would be no savings in that. Who uses these? every residential brand of gas furnace I know of uses a straight up 120 v HSI, not sure about those stupid honeywell smart valves though. Enlighten me plz, i appreciate it
-
11-23-2007, 12:07 AM #15
Professional Member*
- Join Date
- Oct 2006
- Location
- So. NH
- Posts
- 652
I think you might be responding to my post but am not really sure.
My question to skippedover about the incoming electrical service, phase and the operating voltage of the equipment had more to do with what the source of that problem really was, rather than the equipment itself. Electronic equipment does strange things to the sine wave and can't be measured without a true RMS meter. In a perfect world if you have a single or 3 phase system with a balanced load on all phases neutral current will be 0. When you add a buch of electronic loads to the system the power supplies in them clip the sine waves and balance becomes distorted. It does strange things. A non true RMS meter may read zero on a neutral conductor but a true RMS meter could read 500 Amps. That is why neutral conductors of multi wire systems burn up in commercial sytems. I think it may also be migrating to residential systems along with other problems.
-
11-23-2007, 01:58 AM #16
I think jibroni was refering to TinKnocker's statement "with these new ignitors the voltage to them drops to the point where they wont lite to burners then on the next try the voltage is increased to the last recorded voltage the burners lit and remain there till the power is disconnected the starts the search orver again"
I have never heard of this response, but there are a lot things I haven't heard of. Also, if you reduce the voltage to an electric heater (ignitor) the amperage and wattage will decrease I=V/R and W=VxI where R is a fixed value for the ignitor. This is not true for an electric motor.
-
11-23-2007, 06:44 AM #17
Banned
- Join Date
- Dec 2006
- Location
- Middle Tennessee
- Posts
- 11,347
*
agreed;
that is right where i would of started, (unplug the ignitor check voltage and timing voltage was applied and disengaged)
also as others have stated, it is easy enough to change every part in the unit
but why not just use your meter to diagnose the part you are thinking of changing
in this trade (servicework) when performed properly, parts are checked then if proven faulty (with a meter) parts are changed!
.
-
11-23-2007, 07:03 AM #18
Professional Member
- Join Date
- Nov 2007
- Location
- Landisburg,PA
- Posts
- 69
-
11-23-2007, 07:11 AM #19
A manometer would be a help when doing a dianostic on this.
-
11-23-2007, 08:38 AM #20
Professional Member*
- Join Date
- Nov 2001
- Location
- east kansas
- Posts
- 7,969
Some of you guys
need to give this guy a break. Because you are showing your ignorance as how some other equipment works. And some of you should know better.
My gas oven's HSI has to draw a minimum amount of amps before the gas valve to open and stay open.
-
11-23-2007, 08:44 AM #21
Professional Member*
- Join Date
- Nov 2001
- Location
- east kansas
- Posts
- 7,969
Goodman and maybe Lennox used an igniter and board that reduced voltage to the point the furnace would not light. Then on the next attempt the voltage was increased to the last ignition point. (As stated above)
-
11-23-2007, 08:48 AM #22
Banned
- Join Date
- Dec 2006
- Location
- Middle Tennessee
- Posts
- 11,347
-
11-23-2007, 08:54 AM #23
This is most likely not the problem, But get the senor tech to check the condensate piping on this 90%er. if its not draining correct it will try and fire up by sputtering popping but the second pressure switch will not make. Also check the green gound wire that runs behind and routed back of the inducer housing. Its close to the heatexchanger box and I have found them badly burnt giving the gas valve a fit
rick
-
11-23-2007, 08:57 AM #24
Professional Member*
- Join Date
- Nov 2001
- Location
- east kansas
- Posts
- 7,969
Are you sure they don't have a three tries for ignition before a soft lockout?

"Houston, we have a problem"
"Houston, the damn thing locked out again"
"Houston, I turned the key off and back on, it should light now. We can check the problem after the mission, during regular business hours."
-
11-23-2007, 08:59 AM #25
first i take it this is a new furnace
with these newer boards and ignitors the board does reat the ignitor
in some cases
some of the WR boards if you unplug the ignitor to test to see if voltage is been applied or when it is turned of the board will go into default and show ignito fault
you need to check the voltage at the board with every thing intacted
again is it propane or natral gas and what is the manifold pressure
is the ignitor lined up properly and are the burners clear and lined up
after te third valve what did he want to change next
if this is an older unit it may have a weak ignitor or the wrong one
amping the ignitor will give this info. If 3.0 or higher it is good, if less then 3 then time for a new one even if 2.99 it needs to be replace
being you are new then just kick back and watch. ask questions and learn
he isnt going to listen to you from what you are saying here
apply for pro menbership so you can realy learn things the correct way because there is a lot of good info there that cant be posted here
-