    New coil

    I have an inquiry I hope you can help me with. If a new coil is ordered from one of the HVAC companies, should the coil be pressurized with Nitrogen? I could understand the tube ends being plugged to avoid entry of dirt, but if the coil isn't filled with Nitrogen, would there really be a problem with corrosion?

  2. #2
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    68,943
    A new coil should be charged with some inert gas to prevent having moisture in it from the atmosphere.
    Government is a disease...
    ...masquerading as its own cure…
    Ecclesiastes 10:2 NIV


  3. #3
    Join Date
    May 2000
    Location
    Monmouth Junction-NJ-USA
    Posts
    6,002
    How can you be New and Improved at the same time. You are either new or you are improved.??????? Not sure if I believe that you are either. LOL..How you been?????
    If you really know how it works, you have an execellent chance of fixin' er up!

    Tomorrow is promised to no one...

  4. #4
    Join Date
    Mar 2007
    Posts
    3,108
    Most replacement coils are shipped with a holding charge of Nitrogen these days, to prevent air and noncondensibles for entering the coil, and to verify the coil does not leak prior to installation.