    You can plug in ARI reference #'s 1003557 and 1003592 to see performance data on SEER, HSPF, EER, and BTU/H.
  2. #28
    Apr 2004
    I did that too, I wonder why the HSPF is 8.7 in one, and 7.0 in the other?
  3. #29
    Jun 2007
    The Twilight Zone
    Quote Originally Posted by Waterloo View Post
    Is your coil ON TOP of your blower? Should be below the blower. Otherwise, you aren't allowing the heat pump to raise the temperature as well as it should.
    Temperature rise @240V, 1200 CFM:
    4.8KW=13, 7.2KW=19, 9.6KW=25, 14.4KW=38, 19.2KW=50
    The difference between your two aux heat numbers (150 and 136) makes me think that you've got 14.4KW strips. I also think that you might have picked up some radiant heat from the elements/coil. Can you measure it immediately after a turn (perhaps a bypass humidifier duct)?
    Coil is indeed below the fan. Electric strips are above the fan.
    Air handler cfm ranges between 1490 (at .1" static pressure) and 1205 (at .5" static pressure). Not sure what I have, but all-metal ducts and 2 levels of living space (1600 sq ft) makes me think I'm at a low static pressure figure.
    I have 10 kw aux heat for the heat pump, 15 kw total emergency heat.
    I will retest. The 150 degrees seems too high for 10 kw of aux heat. Maybe the t-couple wire was too close to the electric strips for an accurate air temperature.
    Thanx.
  4. #30
    Jun 2007
    The Twilight Zone
    Performance data
    That combination is 35,600 btu cooling, 11.7 EER, 16 SEER, 33,200 btu heating at 47 degrees, 19,900 btu heating at 17 degrees.
    I am not sure why one ARI# lists an 8.2 HSPF while the other lists a 7 HSPF. The heating btus in both ARI#s are exactly the same.
    What is "+TDR" listed after the air handler model#? It's not a TXV, is it?
  5. #31
    DC Metro Area (MD)
    Quote Originally Posted by docholiday View Post
    Could it be for the different stages or would the HSPF not change depending upon which stage it's in?
  6. #32
    Time
    Delay
    Relay
  7. #33
    Jun 2007
    The Twilight Zone
    Time
    Delay
    Relay
    Thank you, beenthere. Appreciate the knowledge.