  1. #14
    Join Date
    Apr 2004
    Posts
    7,680
    16 SEER with only 8.7 HSPF? Someone sold you a system on "efficiency", but forgot to tell you that it was only efficient in cooling mode at mild temperatures. 8.7 HSPF was acomplished by several 10 SEER systems. If you havent made your purchase, spend some time doing some homework.

  2. #15
    Join Date
    Nov 2007
    Posts
    13
    I believe that's what the mktg lit says for it... 3 ton Lennox XP16 which is a 2-speed. Not sure where to get the official stats. I think the only thing better in that line is the XP19 and that I can't afford unless I give up my 3-zoning which is necessary. I do have 20 KW heatstrip backup. Any other recommendation in the Lennox line...all dealers who bid were Lennox.

  3. #16
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,913
    Try some other brands.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  4. #17
    Join Date
    Dec 2006
    Location
    Arkansas
    Posts
    292
    Quote Originally Posted by docholiday View Post
    16 SEER with only 8.7 HSPF? Someone sold you a system on "efficiency", but forgot to tell you that it was only efficient in cooling mode at mild temperatures. 8.7 HSPF was acomplished by several 10 SEER systems. If you havent made your purchase, spend some time doing some homework.
    I don't remember 10 SEER systems having an HSPF of 8.7. Most 13 SEER are below that, typically around 8.2-8.5. What I remember on 10 SEER systems was about 7.7 to 8.2 HSPF. I am going to do a little searching to see if I am wrong.

  5. #18
    Join Date
    Mar 2006
    Location
    The South
    Posts
    2,189
    Quote Originally Posted by stockgal2 View Post
    I believe that's what the mktg lit says for it... 3 ton Lennox XP16 which is a 2-speed. Not sure where to get the official stats. I think the only thing better in that line is the XP19 and that I can't afford unless I give up my 3-zoning which is necessary. I do have 20 KW heatstrip backup. Any other recommendation in the Lennox line...all dealers who bid were Lennox.
    gal,

    The need for a 20kw heat strip backup makes me question whether your HP is sized correctly. Assuming a 3 ton is correct, then I would ask installing dealer about (2) 10kw heat strip modules and have them staged. according to heat loss demand.

    IMO

  6. #19
    Join Date
    Jul 2004
    Posts
    253
    In my opinion, the best procedure with a heat pump is to leave the house set at one temperature. If you dont do this then I suggest getting a thermostat that allows you to lock out the resistance heating strips.


    Quote Originally Posted by dn0121 View Post
    I'll give you an example of how I am using my HP. 70s during day, 61 at night outside temp is above 36 degrees at night and in the upper 40s to mid 50s right now. In the early morning it takes less then an hour for my HP to raise it to 70. I have gas as backup and is locked out above 36 degrees outside temp.

    When you do all electric from what I have read it is not worth it to do temperature swings like I am doing if your in really cold weather. I can't sleep well though with the temp above 65.

  7. #20
    Join Date
    Apr 2004
    Posts
    7,680
    The XP16 in a 3 ton, depending on the match, will only give you between 6.7 and 8.2 HSPF... The EER's are only 10.90 and 11.20 at best. The SEER, as if it were important can only pull a 14.2.

    Dont let them call this a 16 SEER, high effeiciency machine.

    The XP19 is only slightly better on SEER, and maybe even a smidge better on EERand overall average of HSPF , but there is a significant cost difference to gain that little.

  8. #21
    Join Date
    Nov 2007
    Posts
    13
    Choice is either Lennox XP14 which is "up to 16 SEER & up to 9.5 HPSF", or their XP16 w/2-stage scroll compressor "up to 16 SEER & up to 8.7HPSF" both using 410.

    Since I am in semi-mild winter climate with very discounted winter elec rates (8 months of discounted rates), and very very hot summers w/no discounted rate, the XP16 gives me the cost savings when elec rates and burden on system is the worst and giving the 2-stage feature to be able to draw less a/c power instead of full power all the time -- more savings.

    So far the installers questioned between the two as well as Lennox tech preferred the 2-stage feature since again it helps w/summer rates and that the 8.7 HPSF is fine for a heat pump. They all agreed the XP19 doesn't give enough adddl bang for the addl buck.

  9. #22
    Join Date
    Jun 2007
    Location
    The Twilight Zone
    Posts
    2,964
    Quote Originally Posted by stockgal2 View Post
    Choice is either Lennox XP14 which is "up to 16 SEER & up to 9.5 HPSF", or their XP16 w/2-stage scroll compressor "up to 16 SEER & up to 8.7HPSF" both using 410.
    Post model numbers of condenser and air handler for efficiency and performance ratings.

    FYI:
    I measured the supply air temperature (just after the coil) of my Goodman 3 ton 14 SEER (12 EER, 9 HSPF) last night using a Fluke meter w/calibrated t-couple:

    Start
    47 degrees outside
    68 degrees inside
    68 thermostat setpoint

    95.7 air handler temp from heat pump

    Bump stat to 70
    136 degrees (aux heat kicked in)
    96 degree air handler temp after aux heat kicks off and temp stabilzes

    Bump stat to 72
    150 degrees (aux heat must be in 2 stages, 5 kw per stage)
    99.5 degree air handler temp after aux heat kicks off and temp stabilizes

    End test
    72 degree room temp, about 1/2 hour of total run time

  10. #23
    Join Date
    Jun 2007
    Location
    Metro St. Louis
    Posts
    181
    Quote Originally Posted by gary_g View Post
    Post model numbers of condenser and air handler for efficiency and performance ratings.

    FYI:
    I measured the supply air temperature (just after the coil) of my Goodman 3 ton 14 SEER (12 EER, 9 HSPF) last night using a Fluke meter w/calibrated t-couple:

    Start
    47 degrees outside
    68 degrees inside
    68 thermostat setpoint

    95.7 air handler temp from heat pump

    Bump stat to 70
    136 degrees (aux heat kicked in)
    96 degree air handler temp after aux heat kicks off and temp stabilzes

    Bump stat to 72
    150 degrees (aux heat must be in 2 stages, 5 kw per stage)
    99.5 degree air handler temp after aux heat kicks off and temp stabilizes

    End test
    72 degree room temp, about 1/2 hour of total run time
    Is your coil ON TOP of your blower? Should be below the blower. Otherwise, you aren't allowing the heat pump to raise the temperature as well as it should.

    Temperature rise @240V, 1200 CFM:
    4.8KW=13, 7.2KW=19, 9.6KW=25, 14.4KW=38, 19.2KW=50

    The difference between your two aux heat numbers (150 and 136) makes me think that you've got 14.4KW strips. I also think that you might have picked up some radiant heat from the elements/coil. Can you measure it immediately after a turn (perhaps a bypass humidifier duct)?

  11. #24
    Join Date
    Nov 2007
    Posts
    13
    GaryG:
    Lennox models are
    Heat pump: XP16-036 3 ton 16 SEER 2-stage scroll compressor
    Blower coil w/var speed: CBX32MV-036
    Heat strip: 20KW


  12. #25
    Join Date
    Apr 2004
    Posts
    7,680
    "up to" is no different than a commercial for a car where "prices start at". Neither one of them will come into play in the real world. I'm merely suggesting you look for yourself.

  13. #26
    Join Date
    Nov 2007
    Posts
    13
    Understood, that's why i said "up to" as they do. I don't have any literature yet for any other details than what Lennox says on their mktg. Thx

Page 2 of 3 FirstFirst 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event