Results 1 to 13 of 14
    Confused Question-mark curves in ductwork
    We've just had a partial reducting done to get rid of some through-slab ductwork that had become a breeding ground for mold. The installer put a number of question-mark like curves in the new ductwork. What are these curves for?
    I'm assuming there's a good reason for doing this--after all it's more work than running a straight section of duct--but I'm scratching my head as to why it was done this way.
    It is funny looking, and isn't the least restrictive way it could have been done.
    If the ducts are sized to account for all those fittings, it isn't an issue, but that sure is a lot of fittings, lol.
    One issue I have with it is that they sealed all the duct connections with mastic, but didn't seal the joints in the elbows. Unsealed elbows leak, often worse than unsealed duct connections...
    Jun 2007
    Metro St. Louis
    The pipe on the left looks like your trunk run. By doing it this way, he's attempting to keep the branch runs somewhat even. If he had gone strait thru, you would see more airflow out of that duct in comparison to the others.
    Basically, he's trying to keep the effective length of the ducts similar.
    Here and there
    Not seeing the whole system it's hard to tell. The fact they sealed the joints tells me at least they care about quality. Waterloo, do you know a feller named Chuck ?
    No way is that right.
    wouldn't dampers...
    ...do the same thing? I also believe those ducts need to be suspended.
    Quote Originally Posted by Waterloo View Post
    Quote Originally Posted by jpb2 View Post
    They didn't seal the joints in the elbows though...
    My first guess was for flow reduction as there are no dampers anywhere in the system. Second guess is for noise attenuation, however there are already two 90 degree bends between the air handler and trunk.
    I will ask the installer.
    Jun 2007
    Metro St. Louis
    I know two Chucks. One's an uncle in IA. The other is my boss.
    Don't know anyone in the HVAC world by the name of Chuck.
    Apr 2004
    At least they understand that supply runs should not be taken off the ends of the main trunk. It may look goofy, but outside of the mastic missing from the seams in the ells, I wouldnt wory to much about it. At least they didnt run flex.
    Here and there
    Don Heck or Chuck Meadgee ? just a thought.
    Nov 2007
    Chicago
    Quote Originally Posted by docholiday View Post
    Why not run flex if they are just going to install it like that??
    You've got 3 90deg elbows right next to each other and no dampers. That is a huge static pressure drop. Unless the rest of the system is balanced properly [and you mentioned no dampers] there will be little to no airflow through that.
    Apr 2004
    Imagine the inside of a flex with those curves... for a 6" run 10 feet long you'd be lucky to get 50 cfm at the right static and velocity. rounded ells, dont cause that much restriction. Coming off the end would have made a mess of the entire system static.