Transite Ducts and Heat Loss
Results 1 to 3 of 3
  1. #1
    Join Date
    Oct 2005
    Location
    MN
    Posts
    133

    Transite Ducts and Heat Loss

    My Basement (walkout) has transite heat ducts. Manual J heat loss at design load (Minneapolis Minn.)is about 32,000 btu's, at 30 degrees the loss is only about 15,000 btu's. The existing furnace is a 70% 108,000 btu input, about 75,600 out. Seems WAY oversized to me.

    I'm considering replacing existing with a Rheem MOD downflow, and getting different opinions as to size. The original contractor recomends staying with about the same size output. He feels that because of the transite you really need MORE output to overcome the "Cold Ducts" as it takes a while to get everything heated up. The other guy says "downsize". I have about 160 Ln Feet of duct and it is insulated with about R8 foam.

    Because the existing is oversized now, the system does seem to short cycle as far as I'm concerned, and because of this it does blow a lot of cold air every time it starts up. I would think wth a smaller MOD I will get longer run times that would keep the ground temps up and in turn be more comfortable.

    One thing I DO like about this furnace being oversized is that it gives me a backup source of heat when I'm out of town in during Jan/Feb. and would probably keep from having a freeze-up if the main furnace crapped out (Manual J 100,000 btu out).

    Does the transite furnace REALLY need to be oversized to keep up?
    How small dare I go? Smallest MOD is 21,888/54,720 output, next up is 27600/69,000 output, which is not that far off the existing 75,600.

  2. #2
    Join Date
    Feb 2003
    Location
    Huntsville,AL
    Posts
    4,125
    the Transite ducts conduct heat less than almost any other material! --
    [just do not grind the Transite, else get asbestos fibers floating in the air.]
    don't worry about heating the ducts --
    do worry about heating the air.

    where are the ducts located?
    in the ground?
    on the bsmt ceiling?

    are you comfortable now?

    measure the efficiency of the present furnace -- you now have cool | cold weather --

    just curious: how are the bsmt walls insulated?
    Styrofoam on outside?
    harvest rainwater,make SHADE,R75/50/30= roof/wall/floor, use HVAC mastic,caulk all wall seams!

  3. #3
    Join Date
    Oct 2005
    Location
    MN
    Posts
    133
    The ducts are actually a loop of PVC not asbestos and are located under the concrete basement (walkout) floor, there is R-8 foam under and on the sides of the ducts.

    The existing 108,000 btu furnace is 72% efficiency, and has no trouble heating the space even at -20 degrees. In fact to me it seems to short cycle. I'm VERY confident the Manual J of 32,000 btu's is correct.

    The basement is about 2200 sq ft., with about 85 ft of exterior walkout walls with R19 insulation. The remaining walls are CC Block with 2x4 walls and R13 insulation on the interior side.