    Nov 2007
    Beckett Heat Manager Operation
    I have observed the following. The heating system is 4 zones, with tankless water heater, L8124C aquastat, and the Beckett Heat Manager with the DHW temp. probe added. When a thermostat calls for heat the circulator will begin to circulate water but if the heat manager is in economizing mode the circulator will turn off if the boiler temp (per the thrmometer on the boiler) gets to approx 140 deg. The boiler will then stay in this state of burner not running, circulator not running (although the thermostat is calling for heat), and Heat Manager in economizing mode. This state will last several mins until the heat manager switches to Burner Enabled mode. Contacting Beckett they recomend the following aquastat temps -- high temp = 180, low temp = 160 and diff. = 10 deg. (even though the heat manager instructions state that low limit should be 150 deg. or lower). Either low temp setting still yields the same behavior. I am guessing what is happening is the aquastat control is detecting too low a temp which is causing the circulator to stop. Heat manager believes their is still enough heat capacity and therfore preventing the burner from firing. And the stalemate continues until the boiler has lost enough of its heat capacity on its own so the heat manager enables the burner. Is this normal operation with a heat manager? How can this be overcome?
    Jun 2000
    N. W., IN
    If a stat is calling circ. should be running. Heat manager is for burner control and has nothing to do with circ.
    Nov 2007
    Thanks Ron for the reply. That is what my service tech. said too. But when he was checking the system when it went to the state that the stat was calling for heat and circulator stopped, burner not running he created another stat call for heat at the relay and the relay did not even click. None of the circulators would come on. He then turned off the heat manager and the burner fired immediately. He concluded that the low temp should be 150 deg. or lower per the Heat manager instructions. He also had said if thie condition happened again to turn the low limit on the aquastat slightly lower since they are not precise. I'm at 130 deg. now and the condition still happens. Appreciate any thoughts on this.