Carrier/Bryant Help
Results 1 to 10 of 10
  1. #1

    Carrier/Bryant Help

    I bought a new system from a supposed to be reputable dealer. He put in a 4 ton bryant heat pump and a 4 ton coil with a 58mtb 1400 cfm gas furnace. According to the carrier rebate program manager this is to small unit. He said I needed 2000 cfm. My queston is can a new fan be put in this housing?
    Last edited by wormie1205; 11-11-2007 at 09:51 PM.

  2. #2
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,836
    Can it be done,but it could endanger your life,not a good idea.

  3. #3
    Join Date
    May 2007
    Location
    DC Metro Area (MD)
    Posts
    3,366
    6 ton heat pump on a 4 ton coil?

  4. #4

    Dangerous?

    Why is it dangerous to change the fan in the 3.5 t gas unit?

  5. #5

    Goof

    It is a 4 ton coil, and a 4 ton heat pump. The gas furnace is a carrier 96 with a 1400 cfm fan. I mistyped.

  6. #6

    infinity 96

    Why is the gas side of these furnaces so cool? Seems it is warmer on the heat pump side.

  7. #7

    4 ton 4 ton

    Quote Originally Posted by dash View Post
    Can it be done,but it could endanger your life,not a good idea.
    Could I just replace the verible speed fan with a larger one?

  8. #8
    Join Date
    Jun 2001
    Location
    Louisville, KY
    Posts
    12,114
    Why don't you call the local distributor for some assistance IF the dealer won't work with you?
    Perhaps you should have read the instructions before calling.

  9. #9

    er

    most designs in my area at least are 400cfm per ton...so 4 ton=1600 cfm.

    that 1400 cfm gas furnace is a bit low..but 2000cfm is too high..you won't get proper de-hu from the ac in such a case.

    my company designs on 350cfm/ton for cool (for de-hu) and 400cfm/ton for heating and it has worked out nicely for our area.

    just throwing in a different blower isn't the answer..it seems both of those guys are off..if you need 4 tons of heat/cool then you're looking at an airhandler/furnace that needs to push 1600cfm.

    was a proper manual J calculation done on your home? was an infiltrometer test done?

    seems you need to call the install company back and push a warranty on them

  10. #10
    Join Date
    Apr 2007
    Location
    Derwood, Md
    Posts
    142
    Quote Originally Posted by Comfort Queen View Post
    that 1400 cfm gas furnace is a bit low..but 2000cfm is too high..you won't get proper de-hu from the ac in such a case.
    Since the OP did not specifiy the rating for the furnace it can be assumed that the 1400 cfm matches the furnace rating and given the 350 cfm for cooling he should be ok with 1400 cfm for 4 ton/

    I had the reverse happen to me, on my addition the builder's installer installed an oversized furnace with a 1200 cfm unit with a 2 ton AC. Luckily my regular HVAC contractor was able adjust the speed using the lowest available speed. Still not optimal, if I would have known what I know now I would have insisted on a variable speed unit on my addition.