    need help from a pro

    Hey guys, what's up. I hope everyone is doing well. Ive been working as a hvac tech for the past year at a mushroom farm. I got my associates degree in science and completed my hvac-r training at a local tech school... I'm doing well at my job and can figure out most problems but sometimes I wish I had a mentor I could rely on when I'm absolutely confused. Thank you........ Right now I got a couple compressors going off on thermal overload...we cycle are fans to come on at 300 psig and my low side is currently around 40. I'm thinking I got a restricted tev. Any suggestions?

  2. #2
    Join Date
    Apr 2008
    Location
    South New Jersey
    Posts
    131
    Post Likes
    Whats a couple compressors? Is this 2 systems or one 2stage system?

  3. #3
    Join Date
    Apr 2014
    Posts
    29
    Post Likes
    Thread Starter
    One 2 stage system

  4. #4
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,742
    Post Likes
    Compressors cycling on overload is not good. Model # & amperage are needed, along with refrigerant, pressures & temperatures. Along with other things.

  5. #5
    Join Date
    Apr 2008
    Location
    South New Jersey
    Posts
    131
    Post Likes
    I agree.

  6. #6
    Join Date
    Apr 2014
    Posts
    29
    Post Likes
    Thread Starter
    R22. Fan cycles on 300 psig. Superheat is 14. Low side psig is 40... Room is 55 degrees. I weighed in the correct charge according to the nameplate. Condenser coils are clean. Fans working. Filter drier not restricted.

  7. #7
    Join Date
    Apr 2008
    Location
    South New Jersey
    Posts
    131
    Post Likes
    Thermal Overload or The compressors are getting too hot is bad.
    Why do you cycle the fans at 300#? Im guessing the ref. is R-22?
    300psig fan cycle is high in my opinion.

  8. #8
    Join Date
    Apr 2014
    Posts
    29
    Post Likes
    Thread Starter
    Quote Originally Posted by drpsr99 View Post
    Thermal Overload or The compressors are getting too hot is bad.
    Why do you cycle the fans at 300#? Im guessing the ref. is R-22?
    300psig fan cycle is high in my opinion.
    I felt this was high also but it's a standard my "coworkers" go by... They where here before me and that's where they put it.

  9. #9
    Join Date
    Apr 2008
    Location
    South New Jersey
    Posts
    131
    Post Likes
    The space your cooling is 55F??

  10. #10
    Join Date
    Apr 2014
    Posts
    29
    Post Likes
    Thread Starter
    Quote Originally Posted by drpsr99 View Post
    The space your cooling is 55F??
    Yes. The room is 55 and the thermostat is set for 52

  11. #11
    Join Date
    Apr 2008
    Location
    South New Jersey
    Posts
    131
    Post Likes
    Is the liquid line long? What is the size of it ie.1/2 ect.? Is it the correct size for the lenghth of run and unit ton? How do you know the coils are clean- Have you split the outside ones? Have you verified the air filter and INNER evap. is clean? No restrictions on blower blades or caught in wheel? Is the AHU belt drive or direct? How many amps does it draw to name plate amps? After you verify all of that, you may just need a hot gas bypass kit for better capacity control then 300# fan cycle
    especially when your cooling to that low of a temp 52F. But again I would certainly verify all above before the HGB recommendation.

  12. #12
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes
    Give us the model of the condensing units as well. I have a suspicion that you may have some refrigeration condensing units which are misapplied.
    ...like medium temp units for a high temp job.

  13. #13
    Join Date
    Apr 2014
    Posts
    29
    Post Likes
    Thread Starter
    Quote Originally Posted by drpsr99 View Post
    Is the liquid line long? What is the size of it ie.1/2 ect.? Is it the correct size for the lenghth of run and unit ton? How do you know the coils are clean- Have you split the outside ones? Have you verified the air filter and INNER evap. is clean? No restrictions on blower blades or caught in wheel? Is the AHU belt drive or direct? How many amps does it draw to name plate amps? After you verify all of that, you may just need a hot gas bypass kit for better capacity control then 300# fan cycle
    especially when your cooling to that low of a temp 52F. But again I would certainly verify all above before the HGB recommendation.
    Thanks for the reply.. I can tell I like this community already. Yes the size of the pipes are correct. I based that on the fact that we have over 150 units all sized the same way.. as of right now all units are working up to capacity except for this particular unit. The blower is belt driven and I'm getting correct rpm and proper amps....... A couple days ago the pipe coming out from tev was 28 degree and another tech adjusted the tev for it to be 40, now it's overheating... I think he created a restriction?

  14. #14
    Join Date
    Apr 2014
    Posts
    29
    Post Likes
    Thread Starter
    Quote Originally Posted by icemeister View Post
    Give us the model of the condensing units as well. I have a suspicion that you may have some refrigeration condensing units which are misapplied.
    ...like medium temp units for a high temp job.
    Sorry, can you elaborate?

  15. #15
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    14,652
    Post Likes
    Quote Originally Posted by mr.freeze01 View Post
    Sorry, can you elaborate?
    Without the details of what it is you have there I can only speculate but to maintain 52°F your system should be running a lot higher than 40 psig suction...or 17°F SST. The suspicion I have is you have condensing unit designed for a medium temperature application (and they have been purposely holding the suction down to keep them running.) These units will run very high discharge pressures and overload if run much above about 25°F SST. The "normally" high discharge pressures and the other tech's throttling down the TXV are telltale signs.

    I doubt you have regular A/C units because they are intended to run high suction pressures and still maintain reasonable discharge pressures. If you were to run an A/C unit at 40 psig, there's no way it would run at 300 psig unless the condenser were badly plugged up.

  16. #16
    Join Date
    Apr 2014
    Posts
    29
    Post Likes
    Thread Starter
    Quote Originally Posted by icemeister View Post
    Without the details of what it is you have there I can only speculate but to maintain 52°F your system should be running a lot higher than 40 psig suction...or 17°F SST. The suspicion I have is you have condensing unit designed for a medium temperature application (and they have been purposely holding the suction down to keep them running.) These units will run very high discharge pressures and overload if run much above about 25°F SST. The "normally" high discharge pressures and the other tech's throttling down the TXV are telltale signs.

    I doubt you have regular A/C units because they are intended to run high suction pressures and still maintain reasonable discharge pressures. If you were to run an A/C unit at 40 psig, there's no way it would run at 300 psig unless the condenser were badly plugged up.
    Thank you. Yes everyone is always saying that we are asking these units to do something that they were not designed to do lol.. even the owner of the company saids this frequently

  17. #17
    Join Date
    Mar 2014
    Location
    Wichita Falls, TX
    Posts
    40
    Post Likes
    You said you had over hundred of these same units. What does the pressures run on one that is running correctly. The medium temp condensers ought to be all right running at 55. As long as you have a liquid reciever installed on the high side. You should be able to set the txv to 10 super heat right at the end of the evaporator. I too feel that 300 is to high, but it should not cause compressor overload or system malfunction set at 300. Because that is only simulating a little over a hundred degree day.

  18. #18
    Join Date
    Apr 2014
    Posts
    29
    Post Likes
    Thread Starter
    Quote Originally Posted by airknight1 View Post
    You said you had over hundred of these same units. What does the pressures run on one that is running correctly. The medium temp condensers ought to be alright running at 55. As long as you have a liquid reciever installed on the high side. You should be able to set the txv to 10 super heat right at the end of the evaporator.
    Yes. Most units are running at 50-55 low side.we have a accumulator on the lowside that is supposed to prevent liquid coming to compressor. Two stage 10 ton whetherking.

  19. #19
    Join Date
    Feb 2009
    Location
    Manchester, TN
    Posts
    399
    Post Likes
    Sounds like you are working on high temp refrigeration here and not AC. I'll assume the exp valves are set up with the right orifices for this application. For my refrigeration on medium and low temp I usually set my txv 20F below box temp. Not sure if that is 100% correct as I'm self taught on refrigeration. If someone played around with the txv and suddenly the issue starts it's a good indication that is what the problem is. Also 300# is definitely to high for r-22. A regular ac condenser can actually be converted over to work in a refrigeration setting. I don't know why you would do it but I have seen it done. The old guy who did it was crazy genius though.

  20. #20
    Join Date
    Mar 2014
    Location
    Wichita Falls, TX
    Posts
    40
    Post Likes
    Quote Originally Posted by BP1972 View Post
    Sounds like you are working on high temp refrigeration here and not AC. I'll assume the exp valves are set up with the right orifices for this application. For my refrigeration on medium and low temp I usually set my txv 20F below box temp. Not sure if that is 100% correct as I'm self taught on refrigeration. If someone played around with the txv and suddenly the issue starts it's a good indication that is what the problem is. Also 300# is definitely to high for r-22. A regular ac condenser can actually be converted over to work in a refrigeration setting. I don't know why you would do it but I have seen it done. The old guy who did it was crazy genius though.
    Yes a lot of people are dong that now, because its cheaper than a skid. But you need to add the liquid receiver, low and head pressure control. I agree I think his problem is txv.

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •