Results 1 to 2 of 2
    Destroyed combustion chamber
    Comfortmaker oil furnace
    OND150AO2O
    Combustion chamber 20191101
    Combustion chamber found resting on the bottom of primary drum.
    Contractor changed nozzle from 1.25 GPH to 1.00 GPH. Flame is wider and does not hit drum. I use 250 gallons of fuel per year. Unit is 12 years old.
    Where can I find a combustion chamber and is it safe to operate as is?
    Jul 2000
    Northern Wisconsin
    First thing.......... if you had a contractor in that found the combustion chamber out of position or damaged and still fired the furnace.......... find a different contractor! A contractor experienced with oil fired heating equipment will know where to find the combustion chamber and needs to be the one installing it.
    The fiber combustion changer is there for a couple of reasons, the most important one is to protect the metal heat exchanger from damage from the extremely high temperatures produced by the flame. You should not be running this furnace without the combustion chamber in place as it was designed.