    Carrier open rtu controller

    A Trane voyager with tracker system was removed and a Carrier rtu installed with an open rtu controller capable of using 4 different protocols to communicate with the tracker. It came configured for Bacnet @ 17600 baud rate. Couldn't get comm established, tried 9600 baud no luck. Any ideas what I'm missing?

  2. #2
    Join Date
    Jan 2011
    Location
    Bartlesville, Ok
    Posts
    115
    Post Likes
    I believe the Trane Trackers use Lon. And the Trackers frontends I have seen appear to use screen sets specific to their own control boards and points.

  3. #3
    Join Date
    Jan 2013
    Location
    Batavia, New York
    Posts
    15
    Post Likes
    Thread Starter
    That's what I thought too but had no luck with Lon either.

  4. #4
    Join Date
    Jun 2009
    Location
    StL, MO
    Posts
    730
    Post Likes
    Those boards need an option card to do Lon.
    UA LU 562

  5. #5
    Join Date
    Dec 2006
    Location
    Washington, DC
    Posts
    1,068
    Post Likes
    Trane Tracker talks Trane Comm3/Comm4 to the RTU. You will not talk to a Carrier Open RTU. Your only option is to add the RTU card to the Tracker panel. This will allow R,G,Y,W to the RTU.
    Quote Originally Posted by Qui-Gon Jinn (Star Wars Episode 1)
    "The ablilty to speak does not make you intelligent!"

  6. #6
    Join Date
    May 2004
    Location
    SE Pennsylvania
    Posts
    2,617
    Post Likes
    Dont know what version of Tracker you have but this may answer your question, page 22.
    https://www.trane.com/Commercial/Upl...rc010_0618.pdf

  7. #7
    Join Date
    Mar 2012
    Location
    Hamilton Ontario
    Posts
    23
    Post Likes
    Lon-oc is the carrier card


    Sent from my iPad using Tapatalk HD

  8. #8
    Join Date
    Jan 2013
    Location
    Batavia, New York
    Posts
    15
    Post Likes
    Thread Starter
    Thanks for the feedback guys, I was finally put in touch with Mr. Sawyer at Trane controls division who told me the older version of tracker won't communicate with the carrier open no matter what you do. A zn517 or tcm mounted in unit is the only solution. But I saved the best for last while checking out( national acct) the guy at EMS who monitors the Hvacr told me there is a work order in the system to replace all existing controls!! Thought they should have done that when rtu was replaced......

  9. #9
    Join Date
    Mar 2012
    Location
    Hamilton Ontario
    Posts
    23
    Post Likes
    Believe the open controller is bypassed if you use to thermostat terminals and you will lose some function (econimizer)


    Sent from my iPad using Tapatalk HD

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •