+ Reply to Thread
Results 1 to 10 of 10
Thread: Summit BMTX Setup
    Nov 2007
    Question Summit BMTX Setup
    I am trying to access a Summit BCU BMTX thru mini monitor port with hyperterminal. I think I have the correct cord and settings but nothing happens. Any ideas?
    Hanging out in the brewhouse
    Do you have the right cable?
    Beware of the prophet trying to make a profit.
    There is less oxygen from knee level to the floor! Check it out next time you tie your boots.
    Nov 2007
    I am using the 9 pin to rj 12 used for varitrac
    Jul 2001
    maryland
    I think your baud rate should be 38400. Why do you need mini-moniter?
    -JB
    Practically Canadian ehh.
    Quote Originally Posted by chris907 View Post
    Cable is correct one.
    Check you baudrate.
    Nov 2007
    I am setting up a bacnet connection.
    I can try different baud rates.
    If you are setting up the BCU for IP communications use "IP Validation".
    Nov 2007
    I was using IP but I wan't to change to RS232 Bacnet. It used to work for IP but now does not for serial. I assume there is a setting that needs to be changed.
    Jul 2001
    maryland
    It sounds like you want a "hardwired" connection(that's what it's called in Summit). You wouldn't do that thru hyperterminal. Configure your serial port for 38400 open summit and choose hardwired.
    -JB
    Hoboken, New Jersey
    Have you attempted to connect through Ethernet
    Was any of your 5 connection boxes grayed out in your attempt to connect? Also did you check that your comm is off. If you find the file pcarmdrvexe in windows explorer under your tracer summit folder from program files you will see this when you select Bin. If you click it you will get a little DOS screen for about a second. After that you will get your ethernet connections. You should also have the BACNET/IP, Hardwired and Modem options.
+ Reply to Thread
Quick Reply Quick Reply
Register Now
Log-in
  • You may post new threads
  • You may post replies
