    One Yr Old Rheem Malfunctioning

    Model RRPBL030JK06X, 14 seer, 80% AFUE, R410A, Natural Gas Heat, Electric Cool. Professional installation 8/2006.

    Current overnight temps 48F, daytime temps 78F. Set thermostat for 69 to come on at 4am (Heat + Auto Fan). I wake up at 6am to find the house is 62 and the heater is not running. I switch the unit to off then back to Heat and:

    Relay on thermostat clicks
    Unit on roof hums
    Fan does not start
    If I flip the fan from AUTO to ON, it blows cold air. Then flip it back to AUTO and it never starts back up, just hums. Finally at 10:30a it started up and began to blow warm air.

    This is intermittent. It can work fine for days, then one day just won't run right. Sometimes I notice the unit will hum for like 15 or 20 minutes or longer before it starts up. Usually it only hums for like 3 to 5 minutes.

    I want to get the installer out to inspect it, but if it won't malfunction when he is here what can be done?

    Mike
    Sacramento

  2. #2
    Join Date
    May 2007
    Location
    DC Metro Area (MD)
    Posts
    3,371
    I believe you mean the RRPL-B Series, correct? http://www.rheemac.com/products/Prod...icModel=RRPL-B

  3. #3
    Join Date
    Sep 2006
    Location
    Sacramento CA
    Posts
    4
    Quote Originally Posted by RyanHughes
    I believe you mean the RRPL-B Series, correct?
    Yep

  4. #4
    Join Date
    Oct 2007
    Location
    Southern Indiana
    Posts
    94
    Sounds like you need to re-program your t-stat.

  5. #5
    Join Date
    Jul 2007
    Location
    Tulsa, OK
    Posts
    979
    Had a unit drive me nuts once and it ended up being the draft inducer motor hanging up and finally at some point it starts up. Have the tech barely turn the motor and feel for egg shaped bearings etc.

  6. #6
    Join Date
    Jun 2007
    Location
    Round Rock
    Posts
    3,549
    I had a 90 Lennox furnace one time that wouldn't heat above 72. The people wanted it at 75. Usually only at night when coldest outside. I would go to house, it would fire up and run perfectly. The house would heat up to 75 no problem. A few days would pass and they would call complaining. I tore that furnace apart. I decided I would try to heat the house up to 85 one day. After about 1.5 hrs of staring at this stupid furnace, it did it. When the pvc was run through the roof and the roofer wrapped the lead around the pipe to seal the roof (tile roof & new construction) they left a little area of lead partially covering the exhaust. The furnace would run for a while until it built up too much back pressure on the draft inducer motor and shut down on the pressure switch. I climbed on the roof and folded the lead down and haven't been back for that problem in 3 years now.

  7. #7
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,913
    The next time it does it.

    Don't turn the stat off. Call the installing company back out. It has diagnostics.
    If you Turn the stat off you reset the faults. And they won't know what the failure code is.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  8. #8
    Join Date
    Jan 2007
    Location
    in my lumpy chair
    Posts
    1,948
    Quote Originally Posted by beenthere View Post
    The next time it does it.

    Don't turn the stat off. Call the installing company back out. It has diagnostics.
    If you Turn the stat off you reset the faults. And they won't know what the failure code is.
    this is the only advice that is needed here
    I dont warranty Tinkeritus