    Confused Help! How set VisionPro IAQ changeover?

    Okay, how do I select the temp for changeover from heat pump to gas furnace with the IAQ stat? It seems to be set at for 35 outside temp...how do I change it to, say, 30? (Single speed condensor outside, outside IAQ sensor of course, 2 stage 80% VS furnace inside)

    I can't find a thing in the owner's manual on how to do this.

  2. #2
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Installer setup #'s 342,346,350, and 360 are the ones you need to look at.
    350 should be the one you need to change.

  3. #3
    Join Date
    Jun 2003
    Posts
    131
    Post Likes
    Thread Starter
    Thanks for the info! We'll give it a try.