    If a given furnace has a temperature rise of say 30 - 70 degrees, does the fan (VS) vary +/- from its 'set' speed to keep the temperature in that range? Except when starting cold, is the temperature maintained fairly constant?

    If the above assumptions are correct, can the fan set speed be adjusted lower to maintain the temperature near the upper end of the range?

    AM

  2. #2
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,743
    installer must set up the cfm's to the proper settings.

    not sure of other makes but lennox ecm's do not sense temperature rise............. yet.

  3. #3
    Join Date
    Feb 2007
    Posts
    999
    Quote Originally Posted by t527ed View Post
    installer must set up the cfm's to the proper settings.

    not sure of other makes but lennox ecm's do not sense temperature rise............. yet.
    So basically, is the ecm is just ramping up and down between stages and 'off'?

    AM

  4. #4
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,081
    Yep.

    In heating mode, it basically does 2 speeds, that you will notice.
    It will increase its speed as you filter loads up to maintain air flow. But you won't notice it doing that untill the air filter is long past the point it should have been changed.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event