Results 1 to 5 of 5
Thread: cleveland steamer oven
-
10-31-2007, 04:11 PM #1
Professional Member*
- Join Date
- Nov 2001
- Location
- East Texas
- Posts
- 836
cleveland steamer oven
honeywell ignition module s87b. It it not firing, it sounds like it is trying for about 5 seconds and then locks out. Ihave replaced the rod and spark wire.
Cannot see any spark. The flow chart says 2 replace the mod if the fuse is ok...
-
10-31-2007, 05:46 PM #2
google....cleveland steamer.
FILL OUT YOUR PROFILE!!
-
11-01-2007, 10:11 AM #3
Professional Member*
- Join Date
- Nov 2001
- Location
- East Texas
- Posts
- 836
-
11-01-2007, 03:48 PM #4
Are you
getting power to 24 input side?If so then I'd pull spark wire off and go towards ground if no spark,or not very hot,replace control.Also look at the ground,
If you build it they will come,,,they built it and they went.
-
11-01-2007, 03:59 PM #5
Professional Member*
- Join Date
- Nov 2001
- Location
- East Texas
- Posts
- 836
Its working now, out of alignment...


Reply With Quote