    Gentlemen,
    I'm new to HVAC mini split systems. We just received AQV12JA mini split heat pump and have a question regarding the wiring, hope someone can help.
    In the installation manual, it says:
    "The outdoor unit is powered from the indoor unit through the assembly cable."

    Am I misunderstanding this or is this a typo? Isn't the 240V single phase 2 pole run to the outdoor unit, and the indoor unit powered from the outdoor unit via a shielded 16-4 wire?

    The terminal block on the indoor unit is labeled with:
    1(L), 2(N), F1, F2

    Terminal block on the outdoor unit is labeled with:
    F1, F2, 1(L), 2(N), L, N

    Does the 240V 1ph 2p, L1 & L2 land at the outdoor units 1(L) & L? Or am I blowin' it on the terminal nomenclature on this system? Our HVAC guy has done Mitsubishi's but not the Samsung units, could they be that different?

    Any assistance would be greatly appreciated!

  2. #2
    Join Date
    Sep 2004
    Location
    Newbury Berkshire
    Posts
    492
    Post Likes
    If the indoor unit has a power cord hanging out of it then it's power to indoor.

    Cheers

    richard

  3. #3
    Join Date
    Oct 2007
    Location
    Fair Oaks, CA
    Posts
    2
    Post Likes
    Bump . . . anyone?

  4. #4
    Join Date
    Mar 2004
    Location
    Grottoes VA
    Posts
    5,854
    Post Likes
    No DIY can be answered on this site do to forum rules. Sorry.
    Karst means cave. So, I search for caves.

  5. #5
    Join Date
    Feb 2005
    Posts
    66
    Post Likes
    The samsung units are wired different than the Mitsu. or sanyo. I believe you run (5) 14 guage conductors between the indoor & outdoor units, w/ 240 power(2 hots & ground from breaker). No neutral.

  6. #6
    Join Date
    Feb 2005
    Posts
    66
    Post Likes

    Red face

    Oops, sorry K.