    Confused Need Economizer Help

    My company recently installed a rooftop unit at a newly constructed variety store, Its an Allied commercial rooftop unit with an economizer on it, the building is getting a positive pressure and holding the front door open an inch or so from the pressure only while the unit is running, we seemed to think it was the economizer but it seems to be set up properly as per the manufacturers specs. The barometric relief dampers are opening and closing when needed but still getting a positive pressure inside the building im not sure what is going on with the economizer or maybe it is the blower on too high of a speed?? any help would be greatly appreciated I am somewhat of a newcomer 2 and a half years as an apprentice and am working on this myself, Thank you in advance for any help!!!

  2. #2
    Join Date
    Oct 2001
    Posts
    6,939
    is there an exhaust fan on the dampers to pull the return up and discharge it out.if you don'yt ave a unit installed power exhaust the supply fan is BALLOONING the space thats why the doors are being pushed open.
    "when in doubt...jump it out" http://www.youtube.com/watch?v=U1qEZHhJubY

  3. #3
    Join Date
    Mar 2004
    Location
    Austin, Texas
    Posts
    1,959
    What does the TAB report say the air flows are? How do those airflows compare with the design? What is the pressure that is holding the door open (some one needs a micromanometer to measure this pressure)?
    If "I have always done it this way" is a good reason to do it again, how many times do I have to do something wrong - before it becomes right?

  4. #4
    John Culpepper's Avatar
    John Culpepper is offline CHANGE YOUR EMAIL ADDRESS Professional Member*
    Join Date
    Oct 2007
    Location
    Austin Texas
    Posts
    1,776
    Maybe a VFD on blower moter? Had similar problem on rooftop package unit couldn't resolve problem until unit got changed out with Trane Voyager with VFD and hot gas bypass.

  5. #5
    Join Date
    Aug 2006
    Location
    Windsor area Ontario Canada
    Posts
    285
    Whats a VFD ???

    My company does not have a micromanometer....

    The economizer did not come with an exhaust fan for the dampers, ive never seen that before, anyway my boss expects me to fix this problem without adding any equipment, not possible??

  6. #6
    John Culpepper's Avatar
    John Culpepper is offline CHANGE YOUR EMAIL ADDRESS Professional Member*
    Join Date
    Oct 2007
    Location
    Austin Texas
    Posts
    1,776

    Smile

    It is a veriable frequenquincy drive. It controlles how many hertz your motor runz at and controls speed.
    Nemo me impune lacessit.

    How much blood do I have to bathe in to get clean?

    Don't look down on anyone unless you're helping them up.

  7. #7
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    33,884
    From what I've seen, the relief dampers don't have the capacity to relieve the positive pressure from what the economizer can bring in. Is there a way to tell the economizer damper not to open fully to reduce the incoming air?

    What size is the unit?

  8. #8
    du mech eng is offline Professional Member-BM-bad email
    Join Date
    Nov 2003
    Location
    Philadelphia
    Posts
    80
    sounds like you need a power exhauster. is there a lot of return ductwork in the system? barometric relief is best suited for systems with minimal return duct. your supply fan is pressurizing the space enough to push through all of the return ductwork and out the relief damper. the more return duct you have, the higher your space pressure will be. undersized return duct will make this problem even worse.

  9. #9
    numbawunfela's Avatar
    numbawunfela is offline EFC Committee/Professional Member*
    Join Date
    Sep 2007
    Location
    Kenilworth NJ
    Posts
    946
    I'm gonna second the previous post. A power exhauster seems to be required. A power exhauster can be a kit that comes with a unit that is equipped with an economizer. You will likely see installation instructions for it as an option in the paperwork if it is all there in the unit.
    When the economizer opens to get free cooling, it is dumping outside air into the return airstream of the space, presurizing it. A power exhauster is installed in the return and kicks on whenever the economizer opens. then it takes the air in the return duct and throws it outside, so that none of it mixes with the air the economizer brings in. this way you don't pressureize the space, since the proper cfm of air is being provided, and not the proper amount plus a bunch of outside air.

    To know for sure, the front door should stay closed when the econ is closed, and the front door should open when the econ opens.

    Bosses always want miracles, especially when they were the ones who poorly laid out the installation. It may be that the only way to keep the front door closed is to disable the economizer, but you would want the customer involved with that decision, of course.
    Hmmmm....smells like numbatwo to me.

  10. #10
    Join Date
    Aug 2006
    Location
    Windsor area Ontario Canada
    Posts
    285

    Confused

    Heres the situation now, my boss came with me to the site, we closed the economizer fully and the door was till opening therefore the blower is the problem, supplying too much air then its taking out!?!?? There is not much return duct it is a drop ceiling return! So my boss says that we need to slow down the blower, which doesnt make sense to me because if u slow it down ur supplying less but arent you returning less also>?????????????? ok so he wants me to change the pulley on the motor to slow down the motor and he thinks this will fix the problem..... any input is appreciated!!! it is an 8.5 Ton rooftop alliance, 3 phase, belted blower motor

  11. #11
    psmurf is offline Waiting Email Confirmation
    Join Date
    Jul 2002
    Location
    hamilton ont can
    Posts
    109
    IF you closed the econ fully and door then econ is not problem
    SO now you are recirculating inside air,Right? HOW can that force open
    a door? Somehow you are getting air into the space from outside.
    did you put all panels back on unit?Is there another unit for space
    that could be the trouble? Is RTU placed on roof curb correctely?
    That auhta keep you busy for a while!
    Good Luck

  12. #12
    John Culpepper's Avatar
    John Culpepper is offline CHANGE YOUR EMAIL ADDRESS Professional Member*
    Join Date
    Oct 2007
    Location
    Austin Texas
    Posts
    1,776
    If you slow down the blower you may not get enough CFM across the evap coil while the compressors are running.
    Nemo me impune lacessit.

    How much blood do I have to bathe in to get clean?

    Don't look down on anyone unless you're helping them up.

  13. #13
    numbawunfela's Avatar
    numbawunfela is offline EFC Committee/Professional Member*
    Join Date
    Sep 2007
    Location
    Kenilworth NJ
    Posts
    946

    Ruling out the obvious

    Not to sound like a butt,

    BUT does the front door close of it's own accord at all? Are you sure that it's failure to close is an indicator of a problem with the AC and not just a bad door closer, hinges etc.

    Positive pressure often causes front doors not to close, but not always.

    Also You may wish to look for infiltration from the outside through non-ventilation sources. An example that won't help here, but illustrates the point: I know of a large McDonalds that had a really hard time maintaining air flow and cooling. it was on the ground floor of a 50+ story office building. The stairway door was propped open to allow for easy access to drop off garbage, and this 50 story tall staircase had a window on every floor. the solar gain heated up the air in the stair gradually, creating a stack effect, sucking better than 5000 cfm up the staircase, negatively pressurizing the space (opposite your apparent problem) and creating issues with make-up air, and exhaust.

    In short - look outside the box
    Hmmmm....smells like numbatwo to me.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event