    Setback thermostat

    Hi,
    I am having difficulty in understanding how setback saves energy?
    What's the difference in terms of energy savings if I shut down my system instead of setting it at a setback.
    And how correct is this statement :
    "By turning your thermostat back 10°–15° for 8 hours, you can save about 5%–15% a year on your heating bill—a savings of as much as 1% for each degree if the setback period is eight hours long"

    Is there a published paper or article about it?

    Thanks
    M

  2. #2
    Join Date
    Mar 2005
    Location
    Indianapolis, IN
    Posts
    241
    Post Likes
    >I am having difficulty in understanding how setback saves energy?

    With todays furnaces, and AC set as close as possible to hourly gains and losses you probably won't save much at all, as you will need energy and long running times to recover.

    The way I see it, they are for comfort. In the winter can have a little bit warmer in the morning, cooler during day, warmer at nigh, and colder when we sleep.

    In the summer I also like to run low fan at night.

    I know some tstats claim up to 33% ( but this is probably on abandoned house mode)

  3. #3
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,328
    Post Likes

    Hmm

    Quote Originally Posted by manu4ever View Post
    Hi,
    I am having difficulty in understanding how setback saves energy?

    And how correct is this statement :
    "By turning your thermostat back 10°–15° for 8 hours, you can save about 5%–15% a year on your heating bill—a savings of as much as 1% for each degree if the setback period is eight hours long"
    Think about the lack of REAL benefit ...
    ..... 6% of $500 ... a $30 per year savings !
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

  4. #4
    Join Date
    Sep 2002
    Location
    I don't know
    Posts
    3,047
    Post Likes
    Heat loss is directly proportional to the temperature differential between the indoor and outdoor temperature.

    Using a setback thermostat reduces the rate of heat transfer through the building envelope and therefore energy consumption.

    The attachment summarizes a study done which proves that programmable t-stats save energy.

  5. #5
    Join Date
    Sep 2002
    Location
    I don't know
    Posts
    3,047
    Post Likes
    Quote Originally Posted by dan sw fl View Post
    Think about the lack of REAL benefit ...
    ..... 6% of $500 ... a $30 per year savings !



    Has it occured to you that most houses cost $1000+ per year to heat with natural gas?

    Reductions in peak summer electricity demand also have to be considered.

    A basic programmable t-stat only costs $70-$150 unless it's purchased with a huge markup.

  6. #6
    Join Date
    Mar 2007
    Location
    Myrtle Beach, SC
    Posts
    2,976
    Post Likes
    Quote Originally Posted by amd View Post
    Has it occured to you that most houses cost $1000+ per year to heat with natural gas?

    Reductions in peak summer electricity demand also have to be considered.

    A basic programmable t-stat only costs $70-$150 unless it's purchased with a huge markup.
    Installed cost depends on where you are, rspecially contractor labor rates. Heating and cooling costs vary by utility and climate also. There is also the size and insulation levels of the house. setback thermostats also make more sense with oversized equipment. With a properly sized system, you may not have capacity for recovery at design conditions.

    Be careful of making blanket statements.
    Remember, Air Conditioning begins with AIR.

  7. #7
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,328
    Post Likes

    Thumbs up Energy savings .. 1 % / degree ... appropriate

    Quote Originally Posted by amd View Post
    Has it occured to you that most houses cost $1000+ per year to heat with natural gas?

    A basic programmable t-stat only costs $70-$150 unless it's purchased with a huge markup.
    A good HNY programmable thermostat can be procured for $32.

    http://www.lowes.com/lowes/lkn?actio...033&lpage=none

    If you have daytime temperature set at 65'F with setback to 55'F at night (i.e. 6 pm - 6 am), one can save ~ $65 per year in Detroit or Minneapolis.
    ( using an average gas rate of $1.20 / therm)

    Many people would not consider a 10'F set-back after already lowering their high set-point to 65'F and the average savings might be in the $40 range.

    Model house:
    2,000 Square Feet single story with 210 square feet of U-0.55 windows, R-13 walls, R-30 ceiling.

    Minneapolis $1.20 Detroit $1.20
    ____ ____ Therm ____ /Therm Savings ____ Therm /Therm Savings
    ____ 70 ____ 1036 ____ $1,243.20 _ $(62.40) ____ 916 _ $1,099.20 $(68.40)
    ____ 65 ____ 984 ____ $1,180.80 _ _____ _______ 859 _ $1,030.80 $-
    ____ 60 ____ 932 5.3% $1,118.40 _ $62.40 ______ 802 _ $962.40 $68.40
    ____ 55 ____ 880 10.6% $1,056.00 _ $124.80 ____ 746 _ $895.20 $135.60
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

  8. #8
    Join Date
    Feb 2007
    Posts
    1,002
    Post Likes
    Quote Originally Posted by Kevin O'Neill View Post
    ..... With a properly sized system, you may not have capacity for recovery at design conditions.
    Would the fact that a new furnace might have a lower temperature rise than a 20 year old unit, also account for this? Likewise, would newer A/Cs being derated (3 ton unit actually 35,000 BTU) similarly affect recovery?

    If this is true, would it be economically pheasible to have an 11 degree heating setback with a new furnace? My old clunker (oversized) can recover through most of the winter in 40 minutes or less. Would a new, properly sized unit take vastly longer to recover, thereby eliminating (any part/all) savings?

    AM

  9. #9
    Join Date
    Mar 2007
    Location
    Myrtle Beach, SC
    Posts
    2,976
    Post Likes
    Quote Originally Posted by ampulman View Post
    Would the fact that a new furnace might have a lower temperature rise than a 20 year old unit, also account for this? Likewise, would newer A/Cs being derated (3 ton unit actually 35,000 BTU) similarly affect recovery?

    If this is true, would it be economically pheasible to have an 11 degree heating setback with a new furnace? My old clunker (oversized) can recover through most of the winter in 40 minutes or less. Would a new, properly sized unit take vastly longer to recover, thereby eliminating (any part/all) savings?

    AM
    Temperature rise is affected by heating capacity and air flow, not age or efficiency. An oversized furnace has higher standby losses than a properly sized furnace with gravity flue.

    A properly sized AC or furnace takes actual heating or cooling capacity into consideration. Some 3 ton systems will give 37000, some 34000 BTUs, some in between. It depends on what indoor coil you match it to. It has been that way as long as I can remember, about 30 years.
    Remember, Air Conditioning begins with AIR.

  10. #10
    Join Date
    Aug 2007
    Location
    MN
    Posts
    2,686
    Post Likes
    Quote Originally Posted by dan sw fl View Post
    A good HNY programmable thermostat can be procured for $32.

    http://www.lowes.com/lowes/lkn?actio...033&lpage=none

    If you have daytime temperature set at 65'F with setback to 55'F at night (i.e. 6 pm - 6 am), one can save ~ $65 per year in Detroit or Minneapolis.
    ( using an average gas rate of $1.20 / therm)

    Many people would not consider a 10'F set-back after already lowering their high set-point to 65'F and the average savings might be in the $40 range.

    Model house:
    2,000 Square Feet single story with 210 square feet of U-0.55 windows, R-13 walls, R-30 ceiling.

    Minneapolis $1.20 Detroit $1.20
    ____ ____ Therm ____ /Therm Savings ____ Therm /Therm Savings
    ____ 70 ____ 1036 ____ $1,243.20 _ $(62.40) ____ 916 _ $1,099.20 $(68.40)
    ____ 65 ____ 984 ____ $1,180.80 _ _____ _______ 859 _ $1,030.80 $-
    ____ 60 ____ 932 5.3% $1,118.40 _ $62.40 ______ 802 _ $962.40 $68.40
    ____ 55 ____ 880 10.6% $1,056.00 _ $124.80 ____ 746 _ $895.20 $135.60

    sorry but I have switched 2 of these out in the last week because the pins don't make contact for the heat circuit. ain't that a kick in the teeth, both paid for just a service call this summer because they could buy the stat cheaper and install it themselves, then they call me now for no heat, pay another service call, and buy my stat.
    That's why I recommend getting ours, those honeywells are from China.
    the vision pros and focus pros are from USA, but assembled in Mexico(same assemblers anyway)
    You can't fix stupid

  11. #11
    Join Date
    Aug 2007
    Location
    MN
    Posts
    2,686
    Post Likes
    this one is much better, not too much more. http://www.lowes.com/lowes/lkn?actio...056&lpage=none
    we have used the Trane version of this one and no problems.
    You can't fix stupid

  12. #12
    Join Date
    Sep 2007
    Posts
    11
    Post Likes
    Thread Starter
    Thanks for nice insight. Especially the technical report about Canadian houses.
    Of course savings can be achieved from setback, but what this number "8 hrs" from where it is coming, why the setback has to be 8hrs or more to maximize the savings?
    I understand that why setback is preferred over shutting down because of the recovery time, it will take forever to reach back to comfort level temperature am I right? So basically I can save more energy if I shut down the system when not in home but I will be compromising my comfort. What about the difference in energy savings, is the system going to consume more energy if started from shut down state to reach a comfort state as compared to a system which is on a setback and reach a comfort state?

    thanks
    M

  13. #13
    Join Date
    Jun 2006
    Posts
    294
    Post Likes
    This is fairly complicated and will give good results for homes that aren't well insulated. It also depends on the average outside air temp. If you set back say 10 degrees in a poorly insulated home, then the house temp will be lowered by the 10 deg very early in the evening, say 2 hours and the average savings would be
    10*6/24/(Ti-To)
    or for Ti=70 assumed inside setpoint temp
    T0=20 assumed outside temp
    I get 5% savings
    Now if it is better insulated it may take the full 8 hours to lose the 10 degrees so the average loss is 5 degrees and the formula is then
    5*8/24/Ti-To) or
    3%
    Now if the home is extremely well insulated it may not reach the 10 degree loss and the savings would be even smaller.
    So, if you experiment, you substitute the average loss during the night, say dT,and the formula is
    dT*8/24/(Ti-To)

  14. #14
    Join Date
    Apr 2002
    Posts
    11,808
    Post Likes
    Keep your house a little colder in the winter or a little warmer in the summer
    The way we build has a greater impact on our comfort, energy consumption and IAQ than any HVAC system we install.

    http://www.ductstrap.com/

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •