    Carrier 3V Load shedding

    Is it possible to set up load shedding in 3V if so how and where can I find the info on it?

  2. #2
    Join Date
    Mar 2007
    Location
    Melbourne,Aus
    Posts
    346
    The 3V system can be loadshed the same as any CCN system, a loadshed module is required on the network and the Premierlinks controlling the units have to be setup for loadshedding. See the attached, the complete manual was too big to upload.