Thread: Carrier Condenser Explodes!!!

  1. #1
    Join Date
    Oct 2005
    Location
    Pacific Northwest
    Posts
    112
    Post Likes

    Hmm Carrier Condenser Explodes!!!

    I had never seen anything like it before. Maybe somebody else has. The thing that gets me is the system was off, customer wasn't home and the neighbors said that it sounded like a bomb had exploded causing the fire department to be dispatched. R-22 system, ambient was about 80 deg. F

    Name:  temp 001.jpg
Views: 1048
Size:  76.7 KB

    Name:  temp 002.jpg
Views: 904
Size:  61.0 KB

    Name:  temp 003.jpg
Views: 855
Size:  80.7 KB

    Name:  temp 004.jpg
Views: 950
Size:  75.7 KB

    Name:  temp 006.jpg
Views: 886
Size:  62.1 KB

  2. #2
    Join Date
    Jun 2003
    Location
    Florida
    Posts
    9,546
    Post Likes
    Only thing I can think of is someone put oxygen into the system.
    If everything was always done "by the book"....the book would never change.

  3. #3
    Join Date
    Oct 2005
    Location
    Pacific Northwest
    Posts
    112
    Post Likes
    Thread Starter
    Well I have never done that myself, but I hear that if you did put oxygen into a system that contains oil you would probably be found in little pieces. Instant reaction if Im not mistaken.

  4. #4
    Join Date
    Oct 2007
    Location
    Dallas TX
    Posts
    20
    Post Likes
    Maybe a corrosion issue. You can see rust where it (a pressure vessel in essence) blew apart in the last photo.

  5. #5
    Join Date
    Oct 2006
    Location
    houston
    Posts
    80
    Post Likes
    i would have to guess oxygen too but I have never seen it first hand though i sure would like to ka-booom

  6. #6
    Join Date
    Aug 2005
    Location
    San Diego,CA
    Posts
    297
    Post Likes

    Talking

    Cool!
    Sink or Swim!
    A Man has to know his limitations..
    To be old and wise, one must be young and dumb..

  7. #7
    Join Date
    Oct 2005
    Location
    Pacific Northwest
    Posts
    112
    Post Likes
    Thread Starter
    Quote Originally Posted by maximusbravehea View Post
    Maybe a corrosion issue. You can see rust where it (a pressure vessel in essence) blew apart in the last photo.
    yes there is rust present, but in all the cases I've been so lucky to have worked on, which have been subjected to rust or salt air corrosion (or as I call it, Coastal Rot) has one blown up. That sucker blew the jacket on the compressor to shreds.

  8. #8
    Join Date
    Dec 2002
    Location
    omaha
    Posts
    343
    Post Likes
    if no one was home are you sure it was off

  9. #9
    Join Date
    Jan 2006
    Location
    indy
    Posts
    56
    Post Likes
    check contactor. maybe it stuck closed

  10. #10
    Join Date
    Oct 2005
    Location
    Pacific Northwest
    Posts
    112
    Post Likes
    Thread Starter
    Quote Originally Posted by johncavh View Post
    if no one was home are you sure it was off
    very good point. This is what the customer is claiming though. I have thought about this already and the thing that keeps puzzling me is, what if it was running, or what if the condenser fan motor failed with a stuck closed contractor without the customer knowing the compressor was still running and left. Whatever the scenario, I would like to think that the system would have some kind of safety feature to prevent it from violently exploding.

  11. #11
    Join Date
    Oct 2006
    Location
    houston
    Posts
    80
    Post Likes
    the compressor has a high pressure relief that one blew up did they beat someone out of money?

  12. #12
    Join Date
    Nov 2001
    Location
    Port Saint Lucie, FL
    Posts
    1,667
    Post Likes
    I see rust INSIDE the reciever, this problem was caused by improper installation...I.E. air (moisture that contains oxygen) and an arc from compressor motor windings without insulation(degraded by acid) conducted to ground. Was this a 410A system? How did it smell?

  13. #13
    Join Date
    Aug 2006
    Posts
    121
    Post Likes
    My 2 cents here.

    It looks like heavy rusting at the bottom cap of the receiver caused the failure. I guess thats why they caution us about rusted freon or recovery tanks. Although, that receiver looks kind of skimpy on metal thickness.

    It appears to be a suction line receiver, so pressure would (should) be lower if the compressor was operating.

    Great post and pics !!!

  14. #14
    Join Date
    Oct 2007
    Location
    Florida
    Posts
    90
    Post Likes

    Event

    Looks like the accumulator ruptured due to rust, and spun around. There would likely be liquid refrigerant present. The noise could be the sound of the accumulator whacking against the cabinet as it turned, like a playing card in bicycle spokes. Ask the earwitness if it was one short blast, or sustained. Never saw anything like it.

  15. #15
    Join Date
    Jan 2006
    Location
    indy
    Posts
    56
    Post Likes
    it could have been a crank case heater that blew

  16. #16
    Join Date
    Dec 2002
    Location
    Toledo, Ohio, United States
    Posts
    12,974
    Post Likes
    Slick Willis, Twilli wears this when working on carriers

    http://www.global-security-solutions.com/BombSuit.htm
    No Heat No Cool You need Action Fast

  17. #17
    Join Date
    Jul 2000
    Location
    Northern Wisconsin
    Posts
    3,427
    Post Likes
    That's one you want to see AFTER it happens for sure!

    Make sure if you find out any further info that you share it with the rest of us.
    Use the biggest hammer you like, pounding a square peg into a round hole does not equal a proper fit.

  18. #18
    Join Date
    Mar 2006
    Location
    Delaware
    Posts
    448
    Post Likes
    Looks like the accumulator corroded through from the outside and let go, BIG TIME!

    Quote Originally Posted by napoleon-dynomite View Post
    I had never seen anything like it before. Maybe somebody else has. The thing that gets me is the system was off, customer wasn't home and the neighbors said that it sounded like a bomb had exploded causing the fire department to be dispatched. R-22 system, ambient was about 80 deg. F

    Name:  temp 001.jpg
Views: 1048
Size:  76.7 KB

    Name:  temp 002.jpg
Views: 904
Size:  61.0 KB

    Name:  temp 003.jpg
Views: 855
Size:  80.7 KB

    Name:  temp 004.jpg
Views: 950
Size:  75.7 KB

    Name:  temp 006.jpg
Views: 886
Size:  62.1 KB

  19. #19
    Join Date
    Jun 2007
    Location
    Greenville,North Carolina
    Posts
    1,904
    Post Likes
    Quote Originally Posted by twilli3967 View Post
    Slick Willis, Twilli wears this when working on carriers

    http://www.global-security-solutions.com/BombSuit.htm
    Twilli has one of them suits.Twilli use to defuse Bombs.

  20. #20
    Join Date
    Jun 2003
    Location
    Hell Hole Swamp
    Posts
    4,255
    Post Likes
    I work in a coastal area also and have seen accumulators rusted way more than that one, Ive changed countless ones due to corrosion leaks, I have never seen anything remotely close to what happened there, more going on there than just rust

Page 1 of 3 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •