Results 1 to 13 of 14
    CHICAGO SUBURBS
    Dumb chilled water question
    If you have multiple pumps in parralel on a 6 " pipe system, when a second pump is brought on line, what to happens GPM and pressure? I thought the other pumps are for system redundency, however I see places running two or more pumps all the time. If pumps are of equal size and put out equal flow at equal pressure,and the pipe size is the same with one pump or three pumps, I'm trying to figure out what is the advantage to more pumps and how to know when it's time to bring on a second one.I consider my self a good service man but a little lacking in the hot and chilled water department. Thanks Tim
    Some people swear by me and some at me
    Aug 2000
    Under my tree
    Check the pressure drop across your chiller barrel using the manufacturers flow chart for the perticular chiller. This will be a good indication of what is happening. Or get the pump curves.
    To much work with too little time!!!!
    Jan 2003
    San Jose, Ca
    Most plants the second pump is stand by. use only one at a time. some plants use the second pump as load goes up, and some plants start second pump with second chiller.
    You have to know your plant and what was designed to run.
    Old snipes don't die they just loose their steam
    i am glad that you are focusing on the whole plant and not just the chiller. to properly diagnose and service a chiller, you really need to know how the whole plant works together (or at least how it is supposed to work together).
    http://www.bellgossett.com/Press/BG-unparallel.asp
    good luck.
    Ft Worth Tx ( North Richland Hills)
    I once went on a no heat call to Jr High School in Wyoming when the outside air temp was about 15 below....When I entered the bldg it was about 38 degrees inside,naturally they had dismissed school and sent the kids home.
    I went into the boiler room and all 4 Kewanee hot water boilers were running their hearts out on high fire. .... Checked inlet water temp ... 40 degree water
    Checked outlet water temp... 44 degree water!!! checked the hot water pumps .. two 5 hp B&G pumps running fine ... couplers ok...
    Then it dawned on me that one pump must be a back-up (this was my 1st time at this bldg).. so I shut it off... It's a wonder I didn't thermal shock the boilers...but the outlet water temp immediately jumped from 44 to 80 degrees and the loop eventualy warmed to the 180 degree setpoint..... The water was whistling through the boiler so fast it didn't have time to absorb the heat .... just illustrates how important it is to have the correct GPM. I don't know where all those btus went? up the stack? but the tubes must have been overheated since the water wasn't picking them up (btus) wonder why the tubes weren't shocked when I killed the second pump and that 40 degree water slowed down and contacted the tubes?????????
    How can you have any pudding if you don't eat your meat?
    Jul 2001
    VA
    So who piped the chilled water through the boilers? lol
    Quote Originally Posted by Wj Stevens View Post
    LOL guess I did get off topic ... but it does show how gpms can affect system performance.....
    CHICAGO SUBURBS
    Thanks Jay,Snipe,Ozone,and Absrbr. The B&G info was helpful Jay.
    Apr 2005
    CT
    Centrifugal pumps working in paralel increase the GPM not the pressure, pumps working in series increase pressure not GPM.
    I hope this help.
    Hernan
    Mar 2006
    Pasadena, California
    As the last post said Centrifugal pumps in parallel increase GPM and if connected in series increase head.
    Nov 2003
    Philadelphia
    Quote Originally Posted by herschmidt View Post
    I hope this help.
    Hernan
    this is a common misconception. in fact it is what i was taught entering the industry as well. take a look at the graph and the example in the link that jay guy provided. your system curve would have to be perfectly flat for your theory to hold. that means your system pressure loss would have to stay the same as you increase gpm. since this is not true and pressure losses increase as the square of flow, you get the system curve as shown. you pumps will always operate at the intersection of the pump curve and the system curve. so by bringing on a second pump in parallel you will increase both pressure and flow.
    the example in the link shows 15 gpm @ 4.5 ft head with one pump running and 20 gpm @ 8 ft of head with both pumps running. so with one pump operating you are at 75% of design flow and 56% of design head.
    another helpful link...
    http://www.pump-zone.com/articles/52.pdf
    New Mexico
    Years ago I was asked by an engineer "Give me a scientific reason why I put 2 pumps in parallel"
    I felt a trap so I sugested to increase flow.
    "Nope" he said, "Two smaller pumps were cheaper than one big pump"
    Scientific? I guess ecconomics could be a science.
    Anything built to code is built to the minimum legal standard
    You can be anything you want......As long as you don't suck at it.
    SMW Lu49
    Boise, ID
    In a parallel configuration each pump will operate at the same head and they will provide their share of flow at that pressure
    In series pumping the each pump will operate at the same flow and provide their share of the pressure at that flow rate.
    Some of the pitfalls to watch out for in parallel pumping with pumps of unequal pressure is that the pump with the higher pressure can cause a delta-p across the smaller pump which exceeds it’s cutoff pressure…not good.
    In series pumping if the flow capacities are different than the pump with greater capacity can overflow the lesser pump which can result in cavitation by creating pressure drop in the pump instead of a pressure rise.