10-06-2007, 06:26 PM #1
Professional Member
- Join Date
- Aug 2002
- Posts
- 105
Mitsubishi Ductless Splits Mr. Slim
Installed 2 Mitz. Ductless Split today,,,, after leak check, evauation..I asked the Electrician ..I hired........... If it was all set to fire up....

He says go ahead....turn the disconnect...on...
POP
He yells down ...standing in front of the Air Handler
He ended up smokin.. the board on the AH
Has Anyone had any experience with the wiring for these units...
and should I pay this hack...for destoying my payday ?
Now, I will need to contact the supply house on Monday..to replace the board...that he smoked
-
10-06-2007, 06:41 PM #2
What was wrong?
Experience is what you have an hour after you need it.
-
10-06-2007, 07:07 PM #3
Professional Member
- Join Date
- Aug 2002
- Posts
- 105
Well,
He Failed to run a 3 wire...for the power supply///
L1 N L2
He ran ONLY 2 wires...
I may go with another electician...
to fix the problem
pissed m,e off !
-
10-06-2007, 07:50 PM #4
The power supply for the indoor unit?
Aire Serv of SW Connecticut- Gas heat, dual fuel and central a/c systems installed and serviced
-
10-06-2007, 07:52 PM #5
All you need is L1 and L2 and a ground.
The indoor unit gets power from the outdoor unit, maybe he wired 230V to the 12V dc controll going to the indoor unit.
If he did you are F***ed.
As the contractor before any switch get turned on you need to double check all wiring BEFORE you power it up.Last edited by Freezeking2000; 10-06-2007 at 07:54 PM. Reason: added
Aire Serv of SW Connecticut- Gas heat, dual fuel and central a/c systems installed and serviced
-
10-06-2007, 10:59 PM #6
Professional Member
- Join Date
- Feb 2006
- Posts
- 10
Alot of times the outdoor unit is 120V and the electrician are used to using 240V outside
I have had this happen to me twice!!!!!!!!!!!!!!!!. Now I aways check before plugging in the disconnect. Go ahead and order a control board and if the transformer is not part of the board, order a transformer too.
Good LuckLast edited by moose412000; 10-06-2007 at 11:01 PM. Reason: forgot the first statement
-
10-07-2007, 10:01 AM #7
Professional Member
- Join Date
- Aug 2002
- Posts
- 105
I am looking at the schematic for Mitz. MS 15 series
INDOOR UNIT
2 1 N L1
. . . .
. . . .
. . . .
. . . .
. . . .
2 1 N L1 L1 N L2 Ground
outdoor unit . . . .
power
supply
-
10-07-2007, 10:17 AM #8
Professional Member
- Join Date
- Aug 2002
- Posts
- 105
The schematic failed to show up
there is a 12 V dc source
-
10-07-2007, 10:20 AM #9
Professional Member
- Join Date
- Aug 2002
- Posts
- 105
12 V DC (polar)


-
10-07-2007, 10:47 AM #10
After that happened did you ask the electrican if he could read?
The name plate shows correct voltage and the panel is clear as day how to wire the unit!
But who ever is the start up technician was should have check all that before power is energized to the unit.
-
10-07-2007, 12:54 PM #11
Regular Guest
- Join Date
- May 2005
- Location
- Western Kansas
- Posts
- 255
Agreed!...We went out to install a 230 volt 3-phase at a plant, checked voltage at the contactor before startup 440 volts. Turns out the boss missed that on the label of the old condensor and ordered the wrong one. Glad voltage was checked before we fired it up. That comp. would have been screaming (for a few seconds anyway)
-
10-07-2007, 09:29 PM #12
Regular Guest
- Join Date
- May 2007
- Posts
- 30
Model #'s
What model #'s are you installing?
Tom
-
10-07-2007, 10:47 PM #13Aire Serv of SW Connecticut- Gas heat, dual fuel and central a/c systems installed and serviced