AutoPilot,
Okay the boxes are all single duct cooling only. How do you provide heat? Does the AHU have a reheat coil or is there any baseboard radiation? Does this AHU have a morning warm-up mode? If zones require heat during the occupied mode it looks like they have to go to minimum position and thats it.
Typically I see a low supply air temp control scheme with series fan powered boxes. Why is it a problem to use a supply air reset?
What is wrong with using an average temp of some interior and exterior sensors to reset the SAT. If you include the meeting rooms in the average I would think it would be a good start.
What did they require for VAV minimums? 20%, 30% or higher?
Why are they concerned about mold, because you are raising the SAT above 55 deg? Can you trend the space %RH with a return air %RH sensor?
-
10-08-2007, 12:16 AM #15
Professional Member
- Join Date
- Sep 2007
- Location
- Michigan
- Posts
- 290
Return to Engineer
You said way back an engineer was involved, he designed it I'm assuming, he should be directing you what to do. Are the meeting rooms Occupied when your checking the temp? If all your controls are functioning properly (going to min) this all says return to engineer, the fact that it made it on here, says it even more, your banging your head against the wall. Just my two cents but I avoid leaving work with a headache.
There are quite a few possible changes to the system and quite a bit of work. With our company that equates to QUITE a bit of money. The problem is usually found by the control guy... and the control guy doesn't know the design conditions. Maybe it's acceptable for the zone temps to drop so many degrees below set point.
Anyway, I see there is more than one issue. You should put your boxes to full cooling, watch all the dampers, increase the static pressure set point until they all make. It doesn't matter what a mag reads compared to the control sensor, the mag isn't controlling the system. You lkily have a mechanical problem if the fan is at 60Hz and you can't make static, if your just controls that needs to be addressed by someone before you try to fine tune this system. Maybe it's a box that's opened wide open or something but short of an air balancer you can't know if that's it or the fan is flaking out. Anyway I have a project leader who asks me what the balancer was reading on his chilled water DP and what ours transmitter was reading. I want to smack him around a few times because he thinks we should control to the measurement off his gauges.
"Yeah I can figure out whats wrong with it, but you were here first and there isn't room for two, plus it's cold up here, I'll be in the van"

-
10-08-2007, 05:49 AM #16
Regular Guest
- Join Date
- Dec 2006
- Location
- Hartford, Connecticut
- Posts
- 440
-
10-08-2007, 05:02 PM #17
Professional Member
- Join Date
- Sep 2007
- Location
- Under the sea
- Posts
- 205
Guys, thanks for all your help.
The Owner and Engineer have admitted (reluctantly, thanks guys) the space is NOT being used as originally designed. The system is less than a year old. After looking at some trends, one thing they changed was the time schedules for all zones, (was 6am to 7pm) now system is on 24/7.
It appears all over cooling problems started when they switched to 24 hour operation. Half the floor operates 24/7 while the other half is 9-5 6 days a week and all the vav schedules are set for 24/7. The vavs will goto 0 CFM if scheduled off, so they want release the vav schedules back to automatic for the after hours unoccupied offices.
Thanks Again
All your input is appreciated! Great Job.
Seems they always blame the control guys when the tenants complain
-
10-09-2007, 09:02 PM #18
Just like Orion242 said earlier
"Diversity is my guess, ie the AHU total CFM does not equal to the total of the VAVs max CFM. Nothing strange there, at least in our area its pretty common."
You will not make static pressure set point on MOST systems if all the VAV boxes are in full cooling.
Kevin"Profit is not the legitimate purpose of business. The legitimate purpose of business is to provide a product or service that people need and do it so well that it's profitable."
James Rouse
-
10-10-2007, 12:49 AM #19
Professional Member
- Join Date
- Sep 2007
- Location
- Michigan
- Posts
- 290
Since were going to beat the dead horse here, I was going to let it go, but no. I had to read this three times to follow because the there wasn't much logic to the madness. Relating SAT to static readings, then talking about TAB with fan schd on and in unoccupied. Well that should have been a clue there to him. I missed it, but I'm not on the job or being paid to KNOW the sequence, and typical operation. Sounds like there isn't much working relationship between control guy and the AB. We usaully talk to each other so we understand what conditions the system must be in for the balance to take place, and why. In this case, low box CFM flow so everything is controlling and the system can maintain a setpoint. At some point the balancer must have asked "can you put everything to unoccupied" I'd wonder why, MAYBE that's just me. End of me reading this tread since the subject was closed by the guy asking the questions.
"Yeah I can figure out whats wrong with it, but you were here first and there isn't room for two, plus it's cold up here, I'll be in the van"

-
10-14-2007, 01:49 PM #20
First of all I just briefed this, but if you are over-cooling the building with a chilled water system I would think the fix here would be "relatively" simple.
1. You do not have to maintain a certain airflow to protect the equipment as you would in a DX system.
2. If all the zones are satisfied why continue to supply cool air to the zones? If you only have 15 zones then why not monitor the zone temps vs. the setpoints and allow cooling only when a zone needs cooling? Granted you will have to make this somewhat "sensitive" so that when a conference room gets loaded up in a hurry the system can handle it. Maybe you don't have all that data available? Granted this design goes away from a VAV design but why waste the extra energy when the cooling is not needed?
3. I don't know the type of controllers you are using but also why not pass the the supply air temp out from the air handler to each VAV box so if it has the capability it could change it's own airflow settings based on whether or not the VAV controller thinks the plant is in warmup, central plant heat, or cooling mode?
4. I would also look into adjusting your minimum flows on all the boxes to a lower value.