Results 1 to 9 of 9
Thread: McQuay
-
10-03-2007, 09:38 PM #1
Waiting Email Confirmation
- Join Date
- Dec 2006
- Posts
- 183
McQuay
Does anyone have literature on Mcquay
controller MQ-DCU1310-0?
-
10-04-2007, 04:54 PM #2
Professional Member
- Join Date
- Aug 2002
- Location
- Southern NJ
- Posts
- 962
What are you controlling with it? RTU?
I love to Cook...HVAC is a hobby that pays the bills!
-
10-04-2007, 07:02 PM #3
Waiting Email Confirmation
- Join Date
- Dec 2006
- Posts
- 183
YES, RTU....
I am trying to find out if this controller has a
shutdown option. The fire alm goes off and the unit shuts down.
Then the engineer has to go to the unit and cycle power to reset.
Is there a point that has the option for manual or auto reset shutdown?
-
10-04-2007, 11:24 PM #4
Banned
- Join Date
- Mar 2006
- Posts
- 3,641
I cant cross that number to anything. But perhaps this document might help.
-
10-05-2007, 05:19 PM #5
Professional Member
- Join Date
- Aug 2002
- Location
- Southern NJ
- Posts
- 962
All you need is a jumper wire and it will reset automatically. I can't remember the terminal numbers off the top of my head, I will check tomorrow. They stopped wiring for auto reset lately due to liability reasons.
The number of your board isn't the issue (unfortunatly), it's the way the unit is wired.I love to Cook...HVAC is a hobby that pays the bills!
-
10-05-2007, 05:24 PM #6
Professional Member
- Join Date
- Aug 2002
- Location
- Southern NJ
- Posts
- 962
Do you know or can you get the Model number of the unit and post it here?
I love to Cook...HVAC is a hobby that pays the bills!
-
10-09-2007, 09:23 PM #7
Waiting Email Confirmation
- Join Date
- Dec 2006
- Posts
- 183
Mcquay RTU
Model# RPS0505CSA
It has MQ-DCU1310-0 controller in it.
-
10-09-2007, 09:35 PM #8
Waiting Email Confirmation
- Join Date
- Dec 2006
- Posts
- 183
Thanks Freddy,
I found it in the pdf file.
We can reset the alarm by using clear all across the network.
-
10-10-2007, 10:38 PM #9
Banned
- Join Date
- Mar 2006
- Posts
- 3,641


Reply With Quote