Results 1 to 9 of 9
Thread: McQuay
    Dec 2006
    McQuay
    Does anyone have literature on Mcquay
    controller MQ-DCU1310-0?
    Southern NJ
    What are you controlling with it? RTU?
    I love to Cook...HVAC is a hobby that pays the bills!
    Dec 2006
    YES, RTU....
    I am trying to find out if this controller has a
    shutdown option. The fire alm goes off and the unit shuts down.
    Then the engineer has to go to the unit and cycle power to reset.
    Is there a point that has the option for manual or auto reset shutdown?
    Mar 2006
    I cant cross that number to anything. But perhaps this document might help.
    Southern NJ
    All you need is a jumper wire and it will reset automatically. I can't remember the terminal numbers off the top of my head, I will check tomorrow. They stopped wiring for auto reset lately due to liability reasons.
    The number of your board isn't the issue (unfortunatly), it's the way the unit is wired.
    Southern NJ
    Do you know or can you get the Model number of the unit and post it here?
    Dec 2006
    Mcquay RTU
    Model# RPS0505CSA
    It has MQ-DCU1310-0 controller in it.
    Dec 2006
    Thanks Freddy,
    I found it in the pdf file.
    We can reset the alarm by using clear all across the network.
    Mar 2006
    Quote Originally Posted by d_d_c_jci View Post
    Thanks Freddy,
    cool