Results 1 to 13 of 14
    Failed muffler on O6D compressor?
    Can someone tell me how to determine if you have a bad muffler on a recip. compressor?
    Northwest GA
    Well, short of taking it off and examining it there would be no positive way.
    But if you had some problems like say cracked discharge lines or excessive gas pulsation type noise in the piping and maybe found some metal debris in the liquid line drier then you might have a bad muffler among other things.
    Western Wa
    Talking One way I knew...
    ..was when a piece of discharge valve vibrated its way through the can.
    That was about 6 months after I replaced the valves.
    God Bless our Veterans
    God Bless the USA
    Aug 2000
    Under my tree
    Only failures Ive seen where cracks at the stubs into the shell of the muffler, or plugged up with debris and having a high pressure drop.
    To much work with too little time!!!!
    in a tree looking in your window
    Couple of years ago one of my guys calls me and says he thinks he has a bad muffler on a Carrier chiller, compressor trips on high head after a few seconds, here is what I found.
    If you dont stand behind our troops, please feel free...........to stand in front of them.
    UTAH
    Quote Originally Posted by chillrdude View Post
    Nice...ever find the clip?
    Apr 2012
    Paper Street Soap Company
    Too bad it happened on the high side. Had to reclaim it didn't you.
    Ive had that happen but on the suction side 3 times but I see ALOT of 06 comps.
    Have 4 data centers filled with 30 ton Lieberts and 2 data center in Dallas. 23 Lieberts in each data centers with two comps each.
    Plus have some old Carrier 40 ton Condensing units with 06Es in them.
    I blame those foe my back problems.
    Apr 2012
    Your'e wasting your time.
    Does that unit have a big slab condenser coil ?
    If it does they're notorious for poor heat transfer when they start getting corroded.
    Put a water hose on it while its running. Does your head and liquid pressure close up ? Then no discharge restriction.
    The Hot South
    If he's got a 190# pressure drop between the hot gas Line and liquid line, then he's got a restriction somewhere. Putting water on the coil's not going to help.
    Apr 2012
    Im NOT speaking from inexperience. Ive been through that same scenario more than once on those Carrier RTUs with the flat condenseor coils and the 06D comps.
    He'll tear it apart or isolate the coil and find ZERO restriction.
    Lost count on how mamy Carrier RTUs Ive worked on in the last 20 years.
    The hose test just confirms that coil is junk. If its a discharge restriction where would it be ? In the 1 1/8 discharge line coming off the comp ?
    The 5/8 header ? Seriously ?
    If its a restriction a large differential will remain. when you put a hose on it right ?
    It doesnt, the pressures will almost equalize. Its a test.
    And why to discharge restrictions only happen on Carrier RTUs ?
    They dont.
    But they do have crap coils where the aluminum fins turn to dust way roo soon.